TS MTN6215-5910 Strang behavior

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • TS MTN6215-5910 Strang behavior
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2023-03-30 12:41 AM . Last Modified: ‎2024-07-14 11:42 PM

0 Likes
12
1946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-30 12:41 AM

TS MTN6215-5910 Strang behavior

Hello dears,

I have the TS MTN6215-5910 while  during normal use its suddenly restart.

this issue almost happened several times during testing and commissioning, and it will be very noise for the customer and might reject them.

attached Screen shot from the TS showing its FW.

ETS 5 was used in the project.

TS image.jpg

 

 

 

Best Regards,
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Protocols
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2023-04-06 03:04 AM

2 Likes
0
1896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-06 03:04 AM

Hello @IC_Systems 

 

I see three possible options:


1) split the line into 2 and use separate 640mA PS for each line


2) use 1280mA PS instead the 640mA PS


3) install two 640mA PS in parallel in the same line; but this option has restrictions:

- it is possible with our new 640mA PS MTN6513-0102; you would need to have a distance of 200m between the two PS (distance = length of bus cable)
- it is not possible with our old PS MTN684064; this product doesn't allow 2 PS installed in parallel in one bus line
- When using PS from different manufacturer than Schneider Electric you'd need to check with the manufacturer whether it is allowed

See Answer In Context

Reply
Replies 12
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-03-30 02:21 AM

0 Likes
1
1942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-30 02:21 AM

Hello IC-Systems!
Indeed, it sounds pretty strange.
Is it a new device which you program the first time and you see this effects?
Just trying to understand in which direction we need to think to identify the root cause.

 

Kind regards
Thomas

Application Design Engineer
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2023-03-30 06:48 AM . Last Modified: ‎2023-04-02 01:44 AM

0 Likes
0
1938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-30 06:48 AM

Hello @Thomas_Rohde 

Yes its a new product.

I think the issue in the firmware, but when check its compatible with ETS 5 !

Edit: 

Its happened for more than one TS this is the strange behavior its happened when navigate between pages.

 

Best Regards,
Reply
domotiqa
Lt. Commander domotiqa
Lt. Commander

Posted: ‎2023-04-04 01:24 AM

0 Likes
1
1929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-04 01:24 AM

Hi, I had this issue too on a customer building.

When sliding page, after 2 or 3 slide quick, the product sometimes restart.

We use the new 1280ma power supply.

Smarthome & Smartbuilding Expert
Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2023-04-04 01:39 AM

0 Likes
0
1926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-04 01:39 AM

Hello

 

Could be an issue of insufficient power supply. Multitouch Pro takes 28mA from the bus. 

 

As well it could be an issue of overloaded memory when using customized files. Did you upload customised icons or screensaver file?

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2023-04-04 01:42 AM . Last Modified: ‎2023-04-04 02:18 AM

0 Likes
0
1926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-04 01:42 AM

@domotiqa 

How did you solve the problem, in case you did?

Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2023-04-05 12:44 AM . Last Modified: ‎2023-04-05 01:51 AM

0 Likes
0
1911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-05 12:44 AM

hello dears,

the issue is exactly like @domotiqa  said, after several slides quickly, the product sometimes restart.

I separate the devices with sufficient power supply, but If you think it could be an issue of insufficient power supply then I will check each power supply load.

In my case I didn't  upload customized files.

Edit:

I find in one Line the power about 740 while the power supply is 640mA.

I will solve the power supply issue then I will check.

Thank you for the support @Heribert_Dölger 

Best Regards,
Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2023-04-05 02:03 AM

0 Likes
1
1906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-05 02:03 AM

740mA indeed is too high. Hope by that you can solve the problem. 

Reply
domotiqa
Lt. Commander domotiqa
Lt. Commander

Posted: ‎2023-04-06 12:49 AM

0 Likes
0
1901
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-06 12:49 AM

I solved the problem by using the OFF screen delay. So less heat I guess... so electronic are less on pression. For me it s hardware problem. However I should have it on other too (we have 15 touch)

Smarthome & Smartbuilding Expert
Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2023-04-06 02:08 AM

0 Likes
1
1900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-06 02:08 AM

@domotiqa 

Strange that it happens only on one device. What exactly do you mean with "OFF screen delay"? Did you deactivate the screensaver?

Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2023-04-06 02:34 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-06 02:34 AM

Hello @Heribert_Dölger 

I want to solve it by using 1280mA Power supply instead of the 640mA, I have 60 KNX Devices in that line. Do you have other suggestion, while create a new line with new line coupler and power supply is not easy.

Best Regards,
Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2023-04-06 03:04 AM

2 Likes
0
1897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-06 03:04 AM

Hello @IC_Systems 

 

I see three possible options:


1) split the line into 2 and use separate 640mA PS for each line


2) use 1280mA PS instead the 640mA PS


3) install two 640mA PS in parallel in the same line; but this option has restrictions:

- it is possible with our new 640mA PS MTN6513-0102; you would need to have a distance of 200m between the two PS (distance = length of bus cable)
- it is not possible with our old PS MTN684064; this product doesn't allow 2 PS installed in parallel in one bus line
- When using PS from different manufacturer than Schneider Electric you'd need to check with the manufacturer whether it is allowed

Reply
domotiqa
Lt. Commander domotiqa
Lt. Commander

Posted: ‎2023-04-06 09:23 AM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-06 09:23 AM

Yes

Smarthome & Smartbuilding Expert
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore