Hello Dears,Documents
I have KNX DALI GW (MTN6725-0001), when download from the DCA I got Verification error Pop up message for few ECGs.
the verification error message was like sending 270 received 1.
but the ECGs respond when turn it on/off.
so does this verification error cause any issue and require attention?
Link copied. Please paste this link to share this article on your social media post.
Hello @IC_Systems
this message appears if the reported device type does not match the planning.
However, the reported value of 63 or 127 is very unusual.
It means the device type could not be read properly, or the answer was 63 or 127 (which doesn't make much sense).
my proposal:
Drag these faulty ECGs back to the right side
Download (programming) so that they are free again.
Right-click in the right tree and select "Initialize ECG" in the context menu. (The ECG is completely reset)
Then start a "post-installation"
The devices should reappear on the right side.
Now move the mouse and check the device type in the tooltip.
Are all ECGs of the same type or is it possible that the faulty ones are from a different manufacturer?
Link copied. Please paste this link to share this article on your social media post.
Hello IC_Systems!
to "... I got Verification error Pop up ..."
Can you please share a screenshot of the pop up?
Link copied. Please paste this link to share this article on your social media post.
Will share it when I back to the site.
Edit:
Please see attached Screen shoots @Thomas_Rohde
Link copied. Please paste this link to share this article on your social media post.
Hello @Thomas_Rohde
Do you have any update?
is it a serious issue, while the ECGs are working!
Link copied. Please paste this link to share this article on your social media post.
Hello @IC_Systems
this message appears if the reported device type does not match the planning.
However, the reported value of 63 or 127 is very unusual.
It means the device type could not be read properly, or the answer was 63 or 127 (which doesn't make much sense).
my proposal:
Drag these faulty ECGs back to the right side
Download (programming) so that they are free again.
Right-click in the right tree and select "Initialize ECG" in the context menu. (The ECG is completely reset)
Then start a "post-installation"
The devices should reappear on the right side.
Now move the mouse and check the device type in the tooltip.
Are all ECGs of the same type or is it possible that the faulty ones are from a different manufacturer?