BMENOC0301 in slots 2,8,10&11 of BMEXBP1200 limitation
Hi Experts,
Does anyone know the technical reason why if the Ethernet Backplane-port is off on NOC, why it can't be installed in the 'Bus-X only' slots?
Could Control Expert be modified to allow this? And throw a build error if a user attempts to enable the backplane port in one of these slots?
When doing Premium migrations that have multiple ETY cards, this limitation becomes a hassle.
Thanks
- Labels:
-
02. Modicon M580 ePAC
- Tags:
- english
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-14 01:46 PM
My understanding is that the BMENOC0301 requires the Ethernet backplane. This is the ONLY mechanism it uses to communicate to the CPU on the rack.
So installing it in a Bus-X only slot simply would not work (for communication to CPU... which means it would not work fullstop).
I'm unsure what disabling the Ethernet Backplane Port means here, but I suspect it has a nuance that means the Ethernet Backplane port is actually still active, but perhaps it no longer has filtering applied or similar.
Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..