Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Connect devices on Modbus TCP on Modicon MBK MC80

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Connect devices on Modbus TCP on Modicon MBK MC80
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
ciupol
Lieutenant ciupol
9
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Control Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Solved
ltavolari
Crewman ltavolari
Crewman

Posted: ‎2022-02-02 01:44 AM

0 Likes
4
3291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-02 01:44 AM

Connect devices on Modbus TCP on Modicon MBK MC80

Hi All,

I'm new in Schneider's word. I have a Modicon MC80 20310 and I want to connect it on Modbus TCP with some third party devices, using Control Expert Classic. It is possible? If yes, what are the steps? On the user guide and on Training center I've not found nothing for this case. 

Thank you at all.

Labels
  • Labels:
  • 04. Modicon X80 IO
  • 05. Networking & Communication
  • 08. Tools & Resources
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AlastairF
AlastairF Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-02 01:56 AM

0 Likes
3
3289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-02 01:56 AM

Yes, definitely possible.

What devices are you wanting to connect to?

What data do you want to access in the device or will the device be reading from the MC80?

How often do you want to update the data (read from the device)?

 

The devices will have to exist in the same network domain as the MC80 unless to connect via an external router.

The MC80 doesn't support IO Scanning or DTM's or provide DHCP service.

 

If the MC80 is a TCP Client then you would typically use the READ_VAR function.

 

See Answer In Context

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
AlastairF
AlastairF Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-02 01:56 AM

0 Likes
3
3290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-02 01:56 AM

Yes, definitely possible.

What devices are you wanting to connect to?

What data do you want to access in the device or will the device be reading from the MC80?

How often do you want to update the data (read from the device)?

 

The devices will have to exist in the same network domain as the MC80 unless to connect via an external router.

The MC80 doesn't support IO Scanning or DTM's or provide DHCP service.

 

If the MC80 is a TCP Client then you would typically use the READ_VAR function.

 

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

ltavolari
Crewman ltavolari
Crewman

Posted: ‎2022-02-02 02:22 AM

In response to AlastairF
0 Likes
2
3287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-02 02:22 AM

Thank you for your reply.

The device is a Third-party devices developed by my company (Barcode readers). I have ESD file for recognize it on Fieldbus. 

Data sent from the devices to the PLC are strimgs of bit at variable lenght. Data Sent from PLC are Bit used for trig the device reading phase.

Update time is 16 ms.

 

PLC and my device now are in the same subnet.

 

My problem is that I don't know where I have to update ESD file and where I have to insert device in the project.

 

Thank you.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

AlastairF
AlastairF Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-02-02 01:19 PM

In response to ltavolari
0 Likes
1
3263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-02 01:19 PM

ModBus communications doesn't use an EDS file. That is reserved for EIP, CANopen and Profibus (as GSD file).

ModBus does use a data map so you know where the data is located in the ModBus memory map.

 

ModBus data is located in tables.

Old data address for read only bits is 1xxxx1 and upwards, new data address is %I0 and upwards Address 1xxxx1 = %I0

Old data address for read/ write bits is 0xxxx1 and upwards, new data address is %M0 and upwards. Address 0xxxx1 = %M0

Old data address for read only words is 3xxxx1 and upwards, new data address is %IW0 and upwards. Address 3xxxx1 = %IW0

Old data address for read/ write words is 4xxxx1 and upwards, new data address is %MW0 and upwards. Address 4xxxx1 = %MW0

 

Plenty of information on the web about ModBus addressing and the communication commands.
Also plenty of test tools that you can use to simulate the PLC or the field device.

Try ComTest Pro from Baseblock http://www.baseblock.com/PRODUCTS/comtestpro.htm

Also ModRSsim2 https://sourceforge.net/projects/modrssim2/

 

ComTest Pro will give you information on the device response time so you will be able to verify if it can respond within the 16ms. Note that the poll (request) time repetition rate is also governed by the PLC scan time. Your device is updating its data every 16ms but the PLC may only request every 30ms so you won't see every change in data point.

 

Also look at the READ_VAR help in Control Expert.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

ltavolari
Crewman ltavolari
Crewman

Posted: ‎2022-02-14 03:35 AM

In response to AlastairF
0 Likes
0
3244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-14 03:35 AM

Really thanks,

I've solved the issue.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of