"Not Available" in Total Compensated measurements not logging, why?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • "Not Available" in Total Compensated measurements not logging, why?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant

Posted: ‎2018-08-03 05:04 AM . Last Modified: ‎2020-04-22 01:10 AM

0 Likes
7
1880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-03 05:04 AM

"Not Available" in Total Compensated measurements not logging, why?

Hi all!

We are using the loss compensation framework in several ION8650 meters, and we are facing a singular situation that we want to understand better.

We have the document "Transformer / line loss calculations" and use the "Transformer loss only" section. The data from the test sheet is below:

 

 

So when we verify the readings in NORMAL mode it show as "not available", like below:

 

 

but if we verify it in TEST mode, the values are shown, like below:

 

 

BUT, if we put those parameters in an ION8500 meter, it shows values in kW total compensated but shows "not available" only in kVAR total compensated. This behavior occurs in both normal or test mode verification. The big problem is that when it shows "not available", it stops logging the data in revenue log, as shown below in kVARh comp d int:

 

 

Thanks in advance!!!!!

Labels
  • Labels:
  • ION Setup
Tags (2)
  • Tags:
  • ion meter
  • power_losses
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2018-08-09 09:26 AM

0 Likes
1
1849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-09 09:26 AM

Each default Setup Assistant is matched up with a corresponding default device template.  If you customize either, then some type of customization is required.

Looking at the factory 8650 Setup Assistant, it seems for Normal mode, its attempting to show the 2 output registers from the Arithmetic 24 module:

;kW Compensation

Tab1Reg1Tab4Group3Display6=0,0x4A8F

Tab1Reg1Tab4Group3Display6Label=Total Compensated

;kVAR Compensation

Tab1Reg1Tab4Group4Display6=0,0x4AA1

Tab1Reg1Tab4Group4Display6Label=Total Compensated

Verify the formulas and inputs are set properly:

Hold down <Shift> when clicking on the "Inputs" tab and it will show present values (make sure none are N/A).

This is likely either an incorrect Setup Assistant reference (likely caused by framework customization) or some issue within the device's template configuration (either inputs or setup register values).

See Answer In Context

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-05-04 12:10 PM . Last Modified: ‎2020-05-04 01:08 PM

0 Likes
1
1834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-04 12:10 PM

Hello @Ezequiel-PROLUX 

 

Did you still need help with this?  Regarding the N/A, you are correct that VA rated * Imp has to be larger than LWCu in order to calculate the LVCu.

 

As for showing values in test mode vs normal vs Advanced I will need to know a few more details.

 

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 7
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant

Posted: ‎2018-08-08 08:14 AM

0 Likes
0
1849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-08 08:14 AM

Any suggestions??

Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2018-08-09 09:26 AM

0 Likes
1
1850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-09 09:26 AM

Each default Setup Assistant is matched up with a corresponding default device template.  If you customize either, then some type of customization is required.

Looking at the factory 8650 Setup Assistant, it seems for Normal mode, its attempting to show the 2 output registers from the Arithmetic 24 module:

;kW Compensation

Tab1Reg1Tab4Group3Display6=0,0x4A8F

Tab1Reg1Tab4Group3Display6Label=Total Compensated

;kVAR Compensation

Tab1Reg1Tab4Group4Display6=0,0x4AA1

Tab1Reg1Tab4Group4Display6Label=Total Compensated

Verify the formulas and inputs are set properly:

Hold down <Shift> when clicking on the "Inputs" tab and it will show present values (make sure none are N/A).

This is likely either an incorrect Setup Assistant reference (likely caused by framework customization) or some issue within the device's template configuration (either inputs or setup register values).

Reply
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant

Posted: ‎2018-08-15 01:17 PM

0 Likes
0
1849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-15 01:17 PM

Hi Robert!

Thanks!

For the ION8650 I am using the offline template, ION8650AV403_Offlinemeter.exe

I was digging around to find what calculation was throwing the N/A, and I found it in the arithmetic 8 - W+VARCuLoss1.

I am following the document 70072-0153-08 in the "transformer loss only" section, that says to leave kVA rated in 0.

But if I do so, the values are like follow:

Using like 150kVA for the kVA rated and keeping other values, the result is like follow:

the setup registers are the same.

The test sheet used this data:

I noticed that we need errorflag = 1 for this function work, but the S4² is much greater than S3*1000*S5/100, so the SQRT is negative.

Is probably a limit of losses for compensation to work?

Reply
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant

Posted: ‎2018-08-15 01:58 PM

0 Likes
3
1849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-15 01:58 PM

I noticed that we need to have:

kVA rated*%Imp*10 > LWCu Test

But we have a top limit for %Imp and LWCu Test that are not necessary related as the calculation require.

There is a regulation followed by Schneider on this topic?

Reply
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant

Posted: ‎2018-08-20 04:32 AM

0 Likes
0
1849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-20 04:32 AM

One thing that is very curious, is that if I look in TEST  MODE it show values for the "Total Compensated" in both kW and kVAR, but in NORMAL MODE or in Advanced Mode for ION Setup it shows N/A. Keeping those test sheet values that we know aren't OK.

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-05-04 12:10 PM . Last Modified: ‎2020-05-04 01:08 PM

0 Likes
1
1835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-04 12:10 PM

Hello @Ezequiel-PROLUX 

 

Did you still need help with this?  Regarding the N/A, you are correct that VA rated * Imp has to be larger than LWCu in order to calculate the LVCu.

 

As for showing values in test mode vs normal vs Advanced I will need to know a few more details.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant

Posted: ‎2020-05-04 02:05 PM

0 Likes
0
1830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-04 02:05 PM

Hi Charles.

 

No, later I founded a guide to configure losses on ION8650 and the formula was there too.

With Lee's help I could recognize that the input data was wrong.

Thanks.

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of