Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

metsepm5310r and LVCT dimensions

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • metsepm5310r and LVCT dimensions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Koen_Rowies
Koen_Rowies Troubleshooter
Troubleshooter

Posted: ‎2019-07-01 04:52 AM

0 Likes
3
2075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-01 04:52 AM

metsepm5310r and LVCT dimensions

Hello, Can someone tell me where to find technical doc, 3D image of these references? Link in the brochure are deadlinks... And I have a customer who is asking for dimensions of these LCT's https://download.schneider-electric.com/files?p_enDocType=Technical+leaflet&p_File_Name=PLSED310052E... 0.333V 3-in-1 CTs with RJ45 for PM53x0R METSECTV25006 LVCT SolidC 3in1 RJ45 25mmCtr 60A:1/3V METSECTV25010 LVCT SolidC 3in1 RJ45 25mmCtr 100A:1/3V METSECTV25013 LVCT SolidC 3in1 RJ45 25mmCtr 125A:1/3V METSECTV25016 LVCT SolidC 3in1 RJ45 25mmCtr 160A:1/3V METSECTV35006 LVCT SolidC 3in1 RJ45 35mmCtr 60A:1/3V METSECTV35010 LVCT SolidC 3in1 RJ45 35mmCtr 100A:1/3V METSECTV35012 LVCT SolidC 3in1 RJ45 35mmCtr 120A:1/3V METSECTV35013 LVCT SolidC 3in1 RJ45 35mmCtr 125A:1/3V METSECTV35015 LVCT SolidC 3in1 RJ45 35mmCtr 150A:1/3V METSECTV35016 LVCT SolidC 3in1 RJ45 35mmCtr 160A:1/3V METSECTV35020 LVCT SolidC 3in1 RJ45 35mmCtr 200A:1/3V METSECTV35025 LVCT SolidC 3in1 RJ45 35mmCtr 250A:1/3V METSECTV45025 LVCT SolidC 3in1 RJ45 45mmCtr 250A:1/3V METSECTV45030 LVCT SolidC 3in1 RJ45 45mmCtr 300A:1/3V METSECTV45040 LVCT SolidC 3in1 RJ45 45mmCtr 400A:1/3V METSECTV45050 LVCT SolidC 3in1 RJ45 45mmCtr 500A:1/3V METSECTV45060 LVCT SolidC 3in1 RJ45 45mmCtr 600A:1/3V METSECTV45063 LVCT SolidC 3in1 RJ45 45mmCtr 630A:1/3V METSECTV29006 LVCT SolidC 3in1 RJ45 29mmCtr 60A:1/3V METSECTV29010 LVCT SolidC 3in1 RJ45 29mmCtr 100A:1/3V METSECTV29012 LVCT SolidC 3in1 RJ45 29mmCtr 120A:1/3V METSECTV29013 LVCT SolidC 3in1 RJ45 29mmCtr 125A:1/3V METSECTV29015 LVCT SolidC 3in1 RJ45 29mmCtr 150A:1/3V METSECTV29016 LVCT SolidC 3in1 RJ45 29mmCtr 160A:1/3V METSECTV29020 LVCT SolidC 3in1 RJ45 29mmCtr 200A:1/3V METSECTV70080 LVCT SolidC 3in1 RJ45 70mmCtr 800A:1/3V METSECTV70100 LVCT SolidC 3in1 RJ45 70mmCtr 1000A:1/3V METSECTV70125 LVCT SolidC 3in1 RJ45 70mmCtr 1250A:1/3V Br, Koen
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Koen_Rowies
Koen_Rowies Troubleshooter
Troubleshooter

Posted: ‎2019-09-04 07:46 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-04 07:46 AM

The link in the message does'nt work but I have found the dimensions in this link:

https://download.schneider-electric.com/files?&p_enDocType=Instruction%20sheet&p_File_Name=QGH90901-...

 

Br,

 

Koen

See Answer In Context

Reply
Replies 3
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2019-07-12 09:30 AM

1 Like
2
2065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-12 09:30 AM

Hello Koen Rowies, 

 

I hope Fred Miller (offer manager for PM5300 series) shared the MCAD files through Box on last week of June.

https://schneider-electric.app.box.com/folder/80519158925

 

Let me know if you need any other information.

 

Regards, 

Ramasamy N

Reply
Anonymous user
Not applicable

Posted: ‎2019-08-19 09:05 AM

0 Likes
1
2061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-19 09:05 AM

Hi @Koen_Rowies,

 

@Ramasamy_N  helped you to solve your problem. Please click on “Accept as Solution” so other members can find the same solution through the search bar. Thank you!

 

 

 

Reply
Koen_Rowies
Koen_Rowies Troubleshooter
Troubleshooter

Posted: ‎2019-09-04 07:46 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-04 07:46 AM

The link in the message does'nt work but I have found the dimensions in this link:

https://download.schneider-electric.com/files?&p_enDocType=Instruction%20sheet&p_File_Name=QGH90901-...

 

Br,

 

Koen

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore