Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

how to sending total Kwh through calibration pulser module

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • how to sending total Kwh through calibration pulser module
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic ION8650 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Leo1
Leo1
Explorer

Posted: ‎2023-05-11 02:16 PM

0 Likes
10
3787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-11 02:16 PM

how to sending total Kwh through calibration pulser module

Hello SE ION expert:

 

We have a application in BC Hydro using ION8650 sending KYZ pulse output to SCADA RTU device. Now we are facing an issue and need your support:  how to send total Kwh value through calibration pulser module? 

 

Since the calibration pulser module's input register source should be kw, not kwh; but we only have total Kwh in the meter, don't have total Kw.  

 

Is there a way to convert total Kwh to total Kw?

 

Thanks!

Leo

  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
    PowerLogic ION8650 series
View products (1)
Labels
  • Labels:
  • ION8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
DanL Champion
Champion

Posted: ‎2023-05-12 10:51 AM

1 Like
0
3727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-12 10:51 AM

I discussed this design with SERGIO BERTANI and Anant Patel yesterday. They should be contacting you today.

See Answer In Context

Reply
Replies 10
Bojan
Bojan Leader
Leader

Posted: ‎2023-05-11 02:31 PM

0 Likes
3
3778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-11 02:31 PM

Multiply 5-minute interval kWh value by 12 to get kW

Reply
DanL
DanL Champion
Champion

Posted: ‎2023-05-11 02:37 PM

0 Likes
5
3775
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-11 02:37 PM

some things are not clear to me.

it sounds like there are two ION8650 sending KYZ edges via a CalPulser module through digital outputs to two inputs of an external SCADA RTU input accumulator.

Each transition edge sent from the ION meter corresponds to a preset configured quantity of energy.

Energy (kWh) is the integrated power over a period of time. So to compute energy you can multiply the average power over a time interval by the duration...

 

Exactly what problem are you trying to solve? Do you want each meter to be aware of the other meter's accumulated energy? Are you using software over a communications channel?

Reply
Leo1
Leo1
Explorer

Posted: ‎2023-05-11 02:39 PM

0 Likes
2
3771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-11 02:39 PM

Thanks Bojan, could you explain why?

Reply
Leo1
Leo1
Explorer

Posted: ‎2023-05-11 02:53 PM

0 Likes
4
3770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-11 02:53 PM

Hi Dan,

I have two ION8650s: meter1 and meter2, each meter sending 5 minuites interval energy to the other meter through KYZ pulse. I am using calibration pulser module to achieve this, link each meter's kw as its input source. This part has already done.

The other part has a issue:

In meter 1, I am adding meter1's kwh (from meter1's power meter module) with meter2's kwh (received from meter 2's calibration pulser module KYZ pulse output), then I need to send this kwh tot to SCADA RTU device through KYZ pulse. But since calibration pulser module's input should be power, not energy. so not sure how to solve this. 

Reply
Bojan
Bojan Leader
Leader

Posted: ‎2023-05-11 04:15 PM

0 Likes
1
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-11 04:15 PM

1 kW load consumes the same energy in one hour as what 12kW load consumes in 5 minutes. 

Reply
DanL
DanL Champion
Champion

Posted: ‎2023-05-11 04:35 PM

0 Likes
3
3758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-11 04:35 PM

the quick summary as I understand it is:

 

-each 8650 will use a CAP module to pulse measured energy to be counted by the other meter (separate channels for del and rec)

-each meter will add the counted pulses of energy to their own measured energy and log with a DRE the 5 minute interval energy (separate channels for del and rec)

-the change in counted pulses each second corresponds to the power measured by the other 8650

-this power is added to each meter's own measured power and sent to the SCADA accumulator via pulses from another CAP module.

Reply
Leo1
Leo1
Explorer

Posted: ‎2023-05-12 09:34 AM

0 Likes
0
3745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-12 09:34 AM

Hi Bojan, thanks, I will try it out

Reply
Leo1
Leo1
Explorer

Posted: ‎2023-05-12 09:39 AM

0 Likes
2
3744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-12 09:39 AM

Hello Dan,

see my comments below:

 

-each 8650 will use a CAP module to pulse measured energy to be counted by the other meter (separate channels for del and rec)-------yes

-each meter will add the counted pulses of energy to their own measured energy and log with a DRE the 5 minute interval energy (separate channels for del and rec)------------yes

-the change in counted pulses each second corresponds to the power measured by the other 8650-----------the KYZ pulse corresponds to the energy measured by the other 8650, not power;

-this power is added to each meter's own measured power and sent to the SCADA accumulator via pulses from another CAP module.----------- the energy, not power is added to each meter's own energy, I am trying to convert this added energy to power, and sent to SCADA RTU from CAP module. 

Reply
DanL
DanL Champion
Champion

Posted: ‎2023-05-12 09:51 AM . Last Modified: ‎2023-05-12 09:54 AM

0 Likes
1
3743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-12 09:51 AM

Two points to clarify:
1. the *change* in counted pulses each second corresponds to the power measured by the other 8650 (units are kWh/s). Yes, this is also the change in energy each second and equal to the average power over that second.
Assuming the counter module's Scale is configured to convert counted pulses to kWh (scale = kT/1000), the equation to convert pulses-per-second to power (kW) for every second of module operation is:
P [kW] = (counterValue - previousCounterValue) * 3600 [s/h]

 

2. this power is added to each meter's own measured power and sent to the SCADA accumulator via pulses from another CAlibration Pulser module (the CAP module input must be POWER in units of kW).
The energy is ALSO added to each meter's own energy (Integrator output) and logged in a Data REcorder.

Reply
DanL
DanL Champion
Champion

Posted: ‎2023-05-12 10:51 AM

1 Like
0
3727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-12 10:51 AM

I discussed this design with SERGIO BERTANI and Anant Patel yesterday. They should be contacting you today.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore