conzerv EM6436 energy meter not communicating with Modbus

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • conzerv EM6436 energy meter not communicating with Modbus
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All
Related Products
product field
Schneider Electric
PowerLogic PM5000 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sarfraj
Ensign sarfraj
Ensign

Posted: ‎2024-11-06 10:13 PM

0 Likes
14
1337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-06 10:13 PM

conzerv EM6436 energy meter not communicating with Modbus

Hi all,

I have 10 to 20 conzerv Em6436 energy meter. I'm trying to connect these meters with PME. all meters are not communicating with neither MODSCAN, PAS600 or any Modbus master device. I have checked everything ID, Baud rate, Parity bit, stop bit.

CWhatsApp Image 2024-11-07 at 11.15.17.jpegan anyone support me to find a solution.

Please find attached meter image for better understanding.

  • Thumbnail of PowerLogic PM5000 series
    Schneider Electric
    PowerLogic PM5000 series
View products (1)
Labels
  • Labels:
  • PM3000
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-11-13 10:17 AM

0 Likes
1
1176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-13 10:17 AM

If you can test with another device using the exact same setup to isolate whether the issue is with the meter directly (or if its with the comm setup like the USB -> RS-485 converter).

Your 2 wire RS-485 cable should be wired to the bottom connectors as view from the back of the device as shown in the EM6400 User Guide

Robert_Lee_0-1731521469209.png

I believe the + RS-485 terminal is on the left and the negative terminal on the right looking at the back view.



See Answer In Context

Reply
Replies 14
sarfraj
Ensign sarfraj
Ensign

Posted: ‎2024-11-06 10:14 PM

0 Likes
3
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-06 10:14 PM

@Charles_Murison  Could you please support.

Tags (1)
  • Tags:
  • @Ramasamy_N
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-11-07 02:15 AM

0 Likes
1
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 02:15 AM

Hello @sarfraj, 

 

Please tell us more about your architecture.

You want to connect the meters to PME, but how ?

  • Directly in serial to your PME server ?
  • Use the Panel Server as a Gateway for the EM6436 ? Did you enable Modbus Services on the PAS600 ?
  • Other Modbus TCP gateway ?

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-07 08:36 AM

0 Likes
2
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 08:36 AM

Hello @sarfraj ,

Sadly I do not know the EM6000 series of meters so I am unable to help with this meter. Does the meter support modbus? Are there settings you need to check to make sure that what is trying to talk to the meter match? For example, baud rate, parity and number of stop bits. 

 

regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
sarfraj
Ensign sarfraj
Ensign

Posted: ‎2024-11-07 10:42 PM

0 Likes
0
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 10:42 PM

Sir, I'm trying to connect  using Panel server (PAS600) for the Conzerv EM6436 and yes i have enabled Modbus Services.

And i also tried to connect Modscan using serial to USB converter.

 

It's not connecting. Is there anything i can try to communicate meter with RS485 

 

Tags (1)
  • Tags:
  • @Romain_Polette
Reply
sarfraj
Ensign sarfraj
Ensign

Posted: ‎2024-11-07 10:46 PM

0 Likes
1
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 10:46 PM

Hello @Charles_Murison 

yes this meter has RS485 port and settings for ID, Baud Rate and Parity Bit. i have configured correctly, other Model meters e.g. EM6436H,  in the same network communicating succesfully.

Reply
sarfraj
Ensign sarfraj
Ensign

Posted: ‎2024-11-07 10:47 PM

0 Likes
0
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 10:47 PM

Hi, @Charles_Murison , @Romain_Polette 

Do you know anyone in this community who can help to find the solution

 

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-11-08 03:24 AM

0 Likes
1
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-08 03:24 AM

Hello @sarfraj , 

 

Please note that EM6436 is not native to Panel Server. Only recent H version is native.


Please check documentation for this meter.
It seems you need to send full block requests to read correctly the modbus registers (if I understand well):

Romain_Polette_0-1731065046499.png

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
sarfraj
Ensign sarfraj
Ensign

Posted: ‎2024-11-08 10:01 PM

0 Likes
0
1233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-08 10:01 PM

Hi @Romain_Polette  Sir,

 

I tried to connect With panel server as unknown device, it's not connecting.

And tried to read Modbus register values from Modscan using USB converter, it's not connecting you can find attached image for reference.Neemrana meter 2.png

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-11-11 12:21 PM

0 Likes
1
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-11 12:21 PM

Hello @sarfraj , 

None of your Modbus client can reach your device (error = time-out).

Please check if the COM parameters (baudrate, parity, and time out delay) of your USB port are correct.

Same remarque when connecting with Panel Server. Check if increasing timeout improves connection.

 

If you still cannot connect, please check with tech support and forward Panel Server technical logs. More information regarding your issue will be available on the logs.


Regards,  

Romain POLETTE
Solution Architect - France Operations
Reply
sarfraj
Ensign sarfraj
Ensign

Posted: ‎2024-11-13 09:10 AM

0 Likes
0
1183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-13 09:10 AM

Thanks @Romain_Polette,

I tried today doing that too, It's not working.

Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-11-13 10:17 AM

0 Likes
1
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-13 10:17 AM

If you can test with another device using the exact same setup to isolate whether the issue is with the meter directly (or if its with the comm setup like the USB -> RS-485 converter).

Your 2 wire RS-485 cable should be wired to the bottom connectors as view from the back of the device as shown in the EM6400 User Guide

Robert_Lee_0-1731521469209.png

I believe the + RS-485 terminal is on the left and the negative terminal on the right looking at the back view.



Reply
uday_013
uday_013
Cadet

Posted: ‎2024-11-22 03:44 AM

0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-22 03:44 AM

Do try to communicate with parity setting - EVEN, 

Reply
sarfraj
Ensign sarfraj
Ensign

Posted: ‎2024-11-23 03:45 AM

0 Likes
0
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-23 03:45 AM

Hi @Robert_Lee 

I tried another device with same method.

I'm able to get device data.

Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2025-01-07 08:03 AM

0 Likes
0
679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-07 08:03 AM

Hi @sarfraj 

This seems to be strange, can you connect with local technical support team for further investigation? 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of