Hello SE,
I am seeing an issue with analog output module of my ION8650 (FW: 4.40.001),
Source: 229, zero scale 195, full scale 253, Normalized shows 1 which is not correct.
I changed full scale register to 300, Normalized still stay at 1.
See screenshots below:
Please help check it.
Thanks
Leo
Link copied. Please paste this link to share this article on your social media post.
Hello @Liangchen1982 ,
229687.8 much, much, larger than 253, therefore meter is doing exactly what is expected.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Liangchen1982 ,
229687.8 much, much, larger than 253, therefore meter is doing exactly what is expected.
Regards,
Charles