Hello @NishitShah ,
This is not allowed to connect 3PH PowerTag on 3x 1PH MCB. You must follow the install sheet depending on the PowerTag sensor you are installing.
Concerning the mounting of a PowerTag sensor 3P+N on 3x 1P Breaker with Neutral accessible on the panel :
If PowerTag is connected downstream the breaker
You will loss the Voltage Loss alarm feature
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @NishitShah ,
This is not allowed to connect 3PH PowerTag on 3x 1PH MCB. You must follow the install sheet depending on the PowerTag sensor you are installing.
Concerning the mounting of a PowerTag sensor 3P+N on 3x 1P Breaker with Neutral accessible on the panel :
If PowerTag is connected downstream the breaker
You will loss the Voltage Loss alarm feature
Regards,
Link copied. Please paste this link to share this article on your social media post.
Thank you Romain for a Solution.