Hello,
I have a question about wiring for PM5000 or PM8000 connector of voltage input (V1 V2 V3 VN).
Sometime we need to bridge the cable V2 or others to VN according to voltage system.
Can we connect two wires into one hole of VN etc. of the connector?
It seems that its installation guide is described the case of single wire only.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Hello @suzuki-takahir_1
For the PM8000, the equivalent connector for voltage input is Phoenix Contact 1745645. You may be able to find the maximum wire size for 2 conductors from Phoenix Contact website.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @suzuki-takahir_1
For the PM8000, the equivalent connector for voltage input is Phoenix Contact 1745645. You may be able to find the maximum wire size for 2 conductors from Phoenix Contact website.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello Charles Murison,
Thank you very much for your reply.
I confirmed the specification of the Phoenix Contact 1745645 that is described about 2 conductors.
Thank you very much again for your kind information.