Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Hello,
I would like to know if it is possible to configure the IEEE 519 module in the ION7650 and how to incorporate it into the diagram. My firmware version is V4.1.0.0.1.
In my diagram the IEE519 icon does not appear and in Setup Assistant>Power Quality>Advanced PQ I do not see the option to enable it either.
I see that this is necessary to be able to issue the harmonic compilance report.
Regards.
Link copied. Please paste this link to share this article on your social media post.
Hello @DanielCH ,
IEEE519 is not a single module inside any ION meter. there are a number of different modules with different functions that work together to measure, evaluation, calculate, and store information for the Harmonics compliance report.
Newer ION meters like ION9000/PM8000/ION7400 have the template for IEEE 519 already pre-configured with just a few enable registers required to set everything in motion.
There may be a template in PME frameworks folder for IEEE519 harmonic compliance report in PME with ION7650.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @DanielCH ,
IEEE519 is not a single module inside any ION meter. there are a number of different modules with different functions that work together to measure, evaluation, calculate, and store information for the Harmonics compliance report.
Newer ION meters like ION9000/PM8000/ION7400 have the template for IEEE 519 already pre-configured with just a few enable registers required to set everything in motion.
There may be a template in PME frameworks folder for IEEE519 harmonic compliance report in PME with ION7650.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
refer to https://community.se.com/t5/EcoStruxure-Power-Monitoring/TVD-How-can-I-Use-PME-to-Identify-Harmonics... for more information
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.