Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Synchronizing ION 92040 via IRIG-B

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Synchronizing ION 92040 via IRIG-B
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic ION9000

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
ManuelTrebilcock
ManuelTrebilcock Contributor
Contributor

Posted: ‎2021-10-21 09:10 AM

0 Likes
2
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-21 09:10 AM

Synchronizing ION 92040 via IRIG-B

Hello everyone,

 

We are in the design phase of an architecture intended to synchronize 6 ION 92040 via IRIG-B. The time server must be a GE RT430.

In the ION manual is stated that you can connect an IRIG-B source to one of the meter's digital input for IRIG-B synchronization and that you must configure both, the meter's digital input and the meter's clock. I have the following questions: 

  • What's the configuration you have to do?
  • Which technique can be used to transmit the unmodulated code, TTL, RS232, RS485, etc, and how to connect it to the digital input properly?
  • Can you implement a daisy chain connection for the synchronization of all the meters?

 

Beforehand, thank you for your time.

 

 

Best regards,

 

Manuel Trebilcock

  • Thumbnail of PowerLogic ION9000
    Schneider Electric
    PowerLogic ION9000
View products (1)
Labels
  • Labels:
  • ION9000
Tags (3)
  • Tags:
  • english
  • ion9000
  • IRIG-B
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Yut
Yut
Leader

Posted: ‎2021-11-06 04:58 PM

0 Likes
0
2967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-06 04:58 PM

I'm working with the GPS Synchronize for long time. ION meter can do time synchronize as follow.

To serial port, the clock transmits signal in ASCII format such as Truetime/Datum meters can be daisy chain connected via RS-485 fashion network .

To IRIG-B port (On board DI), clock transmits signal in TTL, DCLS whatever the manufacturer of the clock called unmodulated type this can be daisy chain as long as the the total impedance do exceed the clock output capability i.e. 10k ohms in case of the Arbiter brand.

 

For service

If ASCII type, a computer install with Hyper Terminal software or any is needed for monitor the signal.

IF IRIG-B type, an oscilloscope is needed for monitor the signal.

 

Time sync. check can be done using diagnostics module output monitor see ION Reference. 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-10-21 04:57 PM

1 Like
1
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-21 04:57 PM

Hello @ManuelTrebilcock 

 

For the configurations, there are 2 modules I know of that need to be configured. The clock module's time synchronization source and Digital input's mode needs to be set to IRIG-B

 

 

@DanL 

Do you know the answers to the questions:

  • Which technique can be used to transmit the unmodulated code, TTL, RS232, RS485, etc, and how to connect it to the digital input properly?
  • Can you implement a daisy chain connection for the synchronization of all the meters?

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Yut
Yut
Leader

Posted: ‎2021-11-06 04:58 PM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-06 04:58 PM

I'm working with the GPS Synchronize for long time. ION meter can do time synchronize as follow.

To serial port, the clock transmits signal in ASCII format such as Truetime/Datum meters can be daisy chain connected via RS-485 fashion network .

To IRIG-B port (On board DI), clock transmits signal in TTL, DCLS whatever the manufacturer of the clock called unmodulated type this can be daisy chain as long as the the total impedance do exceed the clock output capability i.e. 10k ohms in case of the Arbiter brand.

 

For service

If ASCII type, a computer install with Hyper Terminal software or any is needed for monitor the signal.

IF IRIG-B type, an oscilloscope is needed for monitor the signal.

 

Time sync. check can be done using diagnostics module output monitor see ION Reference. 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.