Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Solar power, inverters, and current transformer saturation.

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Solar power, inverters, and current transformer saturation.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
578
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
narkshark
narkshark Leader
Leader

Posted: ‎2014-08-18 03:34 PM

0 Likes
5
3334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-18 03:34 PM

Solar power, inverters, and current transformer saturation.

Hello everyone,

My question is something that a few customers have asked me over the last two months, and possibly many more times on the technical support team.

My understanding is that current transformers (CT) are recommended to have at least 10% saturation on them. So, a 200A CT should have at least 20A of current or else the readings may not be accurate and/or may just read zero.

What are customers to do when their solar power inverter is producing low amounts of power at dawn, dusk or during adverse weather conditions? Do we have a recommended procedure for that circumstance? Should they write off those times as just not having reliable readings? Are their specialised CTs available?

Thank you for any input.

Tags (5)
  • Tags:
  • ct
  • current
  • dawn
  • dusk
  • inverter
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2014-08-18 03:50 PM

1 Like
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-18 03:50 PM

Check the data sheets for the current CTs.  You may find the limit is much lower than you think if they are measurement class CTs (instead of relay class).  I know that the ION meters do handle and measure some amount above the nominal rating so maybe you can take advantage of that by using under rated CTs to get better accuracy in the low end - it really depends on what dynamic range you require in the actual application and assuming that the CTs still stay reasonably linear above their rating (which may or may not be the case depending on the CT).

There are CTs that are rated to much lower current levels before they get inaccurate but that will probably cost more.  My suggestion is to critically examine the actual requirements for your application and compare them against the current CTs to see if they match.

Another possible suggestion is to change the compensation curve at the lower range.  Maybe a modified version of the transformer loss compensation framework would work in this case (assuming you are using an ION device where this is programmable).

This is an interesting problem.  Please post back with your solution.

See Answer In Context

Reply
Replies 5
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2014-08-18 03:50 PM

1 Like
0
3249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-18 03:50 PM

Check the data sheets for the current CTs.  You may find the limit is much lower than you think if they are measurement class CTs (instead of relay class).  I know that the ION meters do handle and measure some amount above the nominal rating so maybe you can take advantage of that by using under rated CTs to get better accuracy in the low end - it really depends on what dynamic range you require in the actual application and assuming that the CTs still stay reasonably linear above their rating (which may or may not be the case depending on the CT).

There are CTs that are rated to much lower current levels before they get inaccurate but that will probably cost more.  My suggestion is to critically examine the actual requirements for your application and compare them against the current CTs to see if they match.

Another possible suggestion is to change the compensation curve at the lower range.  Maybe a modified version of the transformer loss compensation framework would work in this case (assuming you are using an ION device where this is programmable).

This is an interesting problem.  Please post back with your solution.

Reply
Yut
Yut
Leader

Posted: ‎2014-09-02 08:14 PM

1 Like
2
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-09-02 08:14 PM

Hello Conway,

     I have some installation in 50MW solar farm using ION8800 which has starting current of 1 mA no problem when cloudy. One thing to do, use just right size of CT and recommend the customer to use our high end meters such as ION8800 ION8650 or the ION7x50 are fine.

K. Yut

Reply
narkshark
narkshark Leader
Leader

Posted: ‎2014-09-03 10:21 AM

0 Likes
1
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-09-03 10:21 AM

When you say a starting current of 1mA, does that take into account the accuraccy of the CT itself that is attached?

Does ION7x50 include the ION7350? I happened to see that come up a lot.

Reply
jimbradley
jimbradley Leader
Leader

Posted: ‎2014-09-03 12:03 PM

2 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-09-03 12:03 PM

All the utility standards (ANSI, IEC, Measurement Canada, etc) have a starting current spec where the energy meter must register something within a time period.  Not really an accuracy spec but more a holdover from mechanical meters to ensure the rotor wasn't stuck.

On the accuracy side there is a spec for load current ranging from a x% of rated load to full load (or higher).  Often there is a step in the accuracy where the lighter load is a "looser" spec, eg. 1-10% of rated load is 0.5% and 10-120% of rated load is 0.2 % ( I made these numbers up).

All these specs are meter only, i.e. the test currents are injected directly into the device under test.  The CTs accuracy are a separate issue.  As we all remember form 1st years physic errors in the case will be summed, i.e. Total errors = Meter Error + CT Error.

I'm pretty sure that 7x50 refers to the 7550 and 7650 as these share a hardware platform.  The 7350 would typically be referred to as apart of the 73X0 family, also a common hardware platform.  The 73x0 family will not meet the same specs as the 7x50 family.

Jim

Reply
Grant_IPACS
Grant_IPACS
Mentor

Posted: ‎2018-02-28 10:33 PM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-28 10:33 PM

Just thinking out loud...

At really low production levels, if there is not enough current to cause output in the CT, wouldn't the meter then register 0Wh for the period?

And if it does manage to get an output from the CT, then some Wh would be registered?

If the question is accuracy, isn't that just a factor of the CT & meter class / accuracy?

Or am I missing something?

Grant

Regards

Grant
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore