Measuring solar generation - Bad CT install

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Measuring solar generation - Bad CT install
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: ‎2018-03-01 12:38 AM

0 Likes
6
1578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-01 12:38 AM

Measuring solar generation - Bad CT install

I have managed to somehow get myself into a reasonable size mess created by a local contractor.

Site has 3 buildings, each with rooftop solar.

Architecture is - 2 of the buildings have 1 x EM1350 and 1 x Link 150 each, both buildings are then connected to a ComX510 with a single EM1350 also directly connected to it on the third building.

The site has been "running" for 6 months, and the contractor is now trying to make sense of the ComX data.  The Wh output is well above his expectations, and above figures comparable suggested by the sum of inverter data, which does not have great accuracy.

What I have found is:

  • On BLDG 1, there is a 20kW system, all CT's show up on the diagnostic on the meter as all reversed, I also found 2 x 40A CT's (R & W) and 1 x 125A CT (B).
  • On BLDG 2, there is a 80kW system, all CT's show up on the diagnostic on the meter as all reversed, I also found 2 x 125A CT's (W & B) and 1 x 40A CT (R).
  • On BLDG 3, there is a 120kW system, all CT's show up on the diagnostic on the meter as all correct, with 3 x 200A CT's (R, W & B) .

So I have swapped the CT's and secondaries around so:

  • BLDG 1 has 3 x 40A CT's and revised secondary to shows polarity OK.
  • BLDG 2 has 3 x 125A CT's and revised secondary to shows polarity OK.
  • BLDG 3 as is.

The question the contractor then posed to me is... "is there any way of applying a ratio / offset etc, to the BLDG 1 & 2 historical data to compensate for the CT reversal and incorrect CT on one phase out of the three?"

I believe there may be a considerable rebate at risk if the data is not properly verifiable.

My thought is:

  • BLDG 1 data may be somewhat useable as there is no CT that has gone "over scale".  If anything ComX interval Wh should be less than what was actually produced, due to a lower B phase reading due to 125A CT.
  • BLDG 2 data is probably not salvageable, as anything over ~30% FLC of inverter output will have R phase @ 100% due to 40A CT.  And Wh would be artificially inflated on this basis.
  • BLDG 3 data should be fine.

However if there is a way of salvaging BLDG 2 data I would love to get any of your suggestions.

I also wanted to know why the active power is a positive when the CT's in BLDG 1 & 2 were initially reversed?

Regards

Grant

Regards

Grant
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2018-03-01 02:37 AM

0 Likes
1
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-01 02:37 AM

Hi Grant,

I would start from Meter Wiring Diagnostic Tool (Phasor Diagram, Phasor Tool) ​and modify it to show the output powers after a corrections.

Best regards,

Bojan

Reply
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: ‎2018-03-01 02:29 PM

0 Likes
0
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-01 02:29 PM

Thanks Bojan,

I am confident my changes have corrected the wiring issues, and from now the meters will be OK in their measurements.

Wondering if there is any way to salvage any data gathered over the last 6 months to help them claim their rebates (particularly for BLDG 2)?

Regards

Grant

Regards

Grant
Reply
enrgyautomation
Commander enrgyautomation
Commander

Posted: ‎2018-03-01 04:49 PM

0 Likes
3
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-01 04:49 PM

Hi Grant,

1) Sadly, there is no easy way to alter the historical data within a Com’X. One has to be intrinsically familiar with the inner workings of a Com’X. If you are, and you do play around with the firmware then will you probably not be supported by Schneider. Only safe way is to extract to a .csv and manipulate in Excel.

2) If the CTs were hooked up the wrong way to start, the information gathered by the meters over the period of time will be gobbledegook. Simple. You will not be able to extrapolate any meaningfull data.

Rule of thumb: validate prior to logging

Ksind regards.

Reply
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: ‎2018-03-01 04:55 PM

0 Likes
2
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-01 04:55 PM

Thanks Brahm,

1) We had no intention to modify ComX, just csv data if there may have been some sort of offset / ratio that could be applied.

2) I think the same, but was living in hope.

3) if we had involvement from the start, yes obviously validation is the key, unfortunately we only got involved 6 months down the track.

Thanks

Grant

Regards

Grant
Reply
enrgyautomation
Commander enrgyautomation
Commander

Posted: ‎2018-03-01 05:49 PM

0 Likes
1
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-01 05:49 PM

Hi Grant,

No worries. Yeah folk like us are always in last. I’m battling with contractors / installers at the moment.

Feel your pain. Good luck!!

Kind regards

Reply
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: ‎2018-03-01 05:52 PM

0 Likes
0
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-01 05:52 PM

thanks

Regards

Grant
Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of