How can i read the EnergyDemandLog with modbus on Ion 7330
- Labels:
-
ION7000
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @ycatellier
As Charles mentioned, by following Appendix B and this FAQ, you should be able to retrieve Modbus value of recorder module.
In this example, I was able to retrieve the Energy&Demand recorder data(Data Recorder 1) of ION7330.
Best Regards,
-Mehran
L3 Expert Advanced metering
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @ycatellier
please note that the ION7300 series of meter are obsolete and no longer officially supported. If the meter does support reading logged data with modbus the instructions would be Appendix B starting on page 82 of
https://www.se.com/us/en/download/document/70022-0124-01/
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @ycatellier
As Charles mentioned, by following Appendix B and this FAQ, you should be able to retrieve Modbus value of recorder module.
In this example, I was able to retrieve the Energy&Demand recorder data(Data Recorder 1) of ION7330.
Best Regards,
-Mehran
L3 Expert Advanced metering