How can i read the EnergyDemandLog with modbus on Ion 7330
Link copied. Please paste this link to share this article on your social media post.
Hi @ycatellier
As Charles mentioned, by following Appendix B and this FAQ, you should be able to retrieve Modbus value of recorder module.
In this example, I was able to retrieve the Energy&Demand recorder data(Data Recorder 1) of ION7330.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hello @ycatellier
please note that the ION7300 series of meter are obsolete and no longer officially supported. If the meter does support reading logged data with modbus the instructions would be Appendix B starting on page 82 of
https://www.se.com/us/en/download/document/70022-0124-01/
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @ycatellier
As Charles mentioned, by following Appendix B and this FAQ, you should be able to retrieve Modbus value of recorder module.
In this example, I was able to retrieve the Energy&Demand recorder data(Data Recorder 1) of ION7330.
Best Regards,
-Mehran
L3 Expert Advanced metering