ION9000T HSTC Settings warning in ION Setup when using PTs

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000T HSTC Settings warning in ION Setup when using PTs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All
Related Products
product field
Schneider Electric
PowerLogic ION9000

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Nicholas_Brown
Ensign Nicholas_Brown Ensign
Ensign

Posted: ‎2024-10-08 09:43 AM

0 Likes
3
730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-08 09:43 AM

ION9000T HSTC Settings warning in ION Setup when using PTs

I am under the impression that when setting up the HSTC Magnitude Threshold settings in the ION9000T that we are to only consider the voltage at the meter terminals.  I have an engineer setting up an ION9000T on an MV substation with 2440:120V PTs.  The nominal voltage at the meter is set at 2440V.

 

When configuring the HSTC settings, assuming that our only consideration is for the 120V that will actually be at the Meter terminals, we were going to leave the Magnitude Threshold at 1000V RMS as configured.  However, ION Setup gives us the following warning:

 

"Magnitude Threshold is below the programmed voltage nominal of 2440V and may result in excessive logging...."

 

Any input on if this warning should just be ignored in this instance given that we are using PTs?  Does ION Setup just not consider this situation?  Or, is my understanding of the HSTC Magnitude settings as it relates to PTs incorrect?

 

Thanks for any help.

  • Thumbnail of PowerLogic ION9000
    Schneider Electric
    PowerLogic ION9000
View products (1)
Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-10-08 02:14 PM . Last Modified: ‎2024-10-09 09:38 AM

1 Like
1
688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-08 02:14 PM

I think this is an oversight on ION Setup part as it was not expected to use HSTC with PTs as this may interfere with expected transient detection.  In most cases, the ION9000 would be *directly connected* to the voltages so ratio would be 1:1.

I've made changes to the next version to only compare to the *secondary nominal* which is computed as:

Snominal = (Vnomimal * PTSecondary) / PTPrimary

When the PT Primary secondary are 1:1 (ex. 120:120), Snominal will be equal to Vnominal but in cases where the user wants to use PTs, then it will be usually a lot lower (and will be reported as computed secondary nominal).

In your case if say you tried entering 100 for the RMS field it would show the warning as "computed secondary nominal of 120V".


For now, you can likely ignore the warning.

See Answer In Context

Reply
Replies 3
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-10-08 11:37 AM . Last Modified: ‎2024-10-08 11:39 AM

0 Likes
0
708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-08 11:37 AM

Hi @Nicholas_Brown 

 

Power Meter Module which is named as Regular Power Meter module uses scaling factors
to obtain high-accuracy measurements of primary transformer levels.

 

So, given meter senses PT secondary voltage as 120V, the primary voltage as actual level of field voltage is taken into account based on the configured PT ratio. Therefore, an incorrect nominal value or threshold level, such as 1000V while Primary is 2440V, will cause the meter to enter an incident state, results in excessive logging.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-10-08 02:14 PM . Last Modified: ‎2024-10-09 09:38 AM

1 Like
1
689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-08 02:14 PM

I think this is an oversight on ION Setup part as it was not expected to use HSTC with PTs as this may interfere with expected transient detection.  In most cases, the ION9000 would be *directly connected* to the voltages so ratio would be 1:1.

I've made changes to the next version to only compare to the *secondary nominal* which is computed as:

Snominal = (Vnomimal * PTSecondary) / PTPrimary

When the PT Primary secondary are 1:1 (ex. 120:120), Snominal will be equal to Vnominal but in cases where the user wants to use PTs, then it will be usually a lot lower (and will be reported as computed secondary nominal).

In your case if say you tried entering 100 for the RMS field it would show the warning as "computed secondary nominal of 120V".


For now, you can likely ignore the warning.

Reply
Nicholas_Brown
Ensign Nicholas_Brown Ensign
Ensign

Posted: ‎2024-10-09 06:46 AM

0 Likes
0
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-09 06:46 AM

Thank you very much.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of