Hi to all!
I have problem with Partial energy reset on a iEM3165 meter.
From the manual i read that is simply necessary write 2020 on the AnalogValue command.
I did, but the energy is not resetting.
As the screenshot attached you can see the AnalogValue is correctly writed, but the Partial Energy is the same.
I use Niagara Workbench as client and the Meter is connected to an Honeywell Controller.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Hi to all!
I figured out that the problem is on Controller side.
I make a mistake writing the Bacnet point with different version between Workbench and Controller OS.
Now is possible to close the case