Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
Rjhar60
Rjhar60
Explorer
Posted: ‎2024-10-02 06:01 PM
1076
I have  3 phase 4 wire 5600 meter on a 208 volt building service and have been getting low kw readings. The configuration is correct. The CT's and associated equipment all checks out. Any ideas??
  • ION Setup
Charles_Murison
Champion
Posted: ‎2024-10-03 08:27 AM . Last Modified: ‎2024-10-03 08:28 AM
1061
Hello @Rjhar60 ,
There are a few common reasons why you might see this.
A) CT polarity is reversed for 1 or more CTs
B) CT connected to a different phase than voltage. Example: phase A voltage has Phase B CT
C) CT shorting block is such that current signal is not reaching the meter.
D) CT and PT ratios are not correct.
E) Other
Some information that would be very helpful.
Per phase voltage readings
Per phase current readings
Per phase power readings
Per phase power factor readings
Phase angles between voltage and current for each phase
Total power readings
Charles
Charles_Murison
Champion
1062
Hello @Rjhar60 ,
E) Other
Charles
Rjhar60
Rjhar60
Explorer
Posted: ‎2024-10-10 05:11 AM
Your reply was helpful.  We ended up finding that the meter pan was wired incorrectly for the E5600 meter We were using.