Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION7400 consider until Harmonic 63th

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7400 consider until Harmonic 63th
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
JhimmyJMQT1
JhimmyJMQT1
Explorer

Posted: ‎2024-06-19 01:22 PM

0 Likes
7
3437
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-19 01:22 PM

ION7400 consider until Harmonic 63th

Dear Experts,

I hope you are doing well. I am writing to you today to seek your expertise regarding a query raised by a client concerning the ION 7400 power meter and its ability to accurately measure power and energy parameters under the presence of harmonic distortions up to the 63rd order.

The client specifically inquired about the accuracy of the ION 7400's measurements when subjected to such harmonic distortions. They expressed concern that the presence of these distortions might compromise the reliability and validity of the meter's readings.

I have conducted some research on the relevant standards, including IEC 62053-22 and ANSI C12.1, but I have not been able to find a definitive answer to the client's question. 

 

I would greatly appreciate your insights on the following:

  1. Can the ION 7400 accurately measure power and energy parameters under the presence of harmonic distortions up to the 63rd order?

  2. If so, what is the level of accuracy that can be expected under these conditions?

Thank you for your time and attention to this matter. I look forward to hearing from you soon.

Juan Quintanilla.

Labels
  • Labels:
  • ION Guidebooks
  • Power Quality
Tags (2)
  • Tags:
  • english
  • ion7400
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
DanL Champion
Champion

Posted: ‎2024-10-10 09:00 AM . Last Modified: ‎2024-10-10 09:01 AM

0 Likes
0
3095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-10 09:00 AM

Yes for the most part, the ION7400 provides quantities following the IEEE 1459 recommended algorithms for power. Some of the 1459 definitions are not provided by default, but the ION7400 can be easily configured to provide most of those. Was there a specific calculation or definition you are interested in?

The Power Meter module performs time domain calculations using 512 samples per (fundamental) cycle.

The Power Harmonics module performs frequency domain calculations up to the 63rd harmonic.

See Answer In Context

Reply
Replies 7
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-06-19 04:14 PM . Last Modified: ‎2024-06-19 04:20 PM

1 Like
0
3413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-19 04:14 PM

Hello @JhimmyJMQT1,

 

These questions are not as simple as one might think at first glance. I can give some context behind what the meter does. To start, the meter has more than 1 power reading. There is fundamental frequency power and other. I say other as there are some settings in places that will dictate the meter's calculations.

 

kVAR has a setup register "UseFundkVAR" that determine if the meter uses fundamental frequency for kVAR calculations. For the active power, are you expecting harmonics on voltage current or both? For example, if voltage has no harmonics but current has 20% THD, The active power is equal to fundamental voltage dot product with fundamental current. 

kVA has 2 options, vector summation or scaler summation.

When Schneider gives an accuracy rating, there is a standard that needs to be reference. If you have a specific standard in mind we can discuss further.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
JhimmyJMQT1
JhimmyJMQT1
Explorer

Posted: ‎2024-06-20 07:59 AM . Last Modified: ‎2024-06-20 07:59 AM

0 Likes
4
3399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-20 07:59 AM

Hello @Charles_Murison ,

 

Thank you for your attention to my previous query. I would like to know which standard I can use to resolve this issue, as the IEC 62053-22 and ANSI C12.1 standards have not provided me with the information I was looking for.

 

I believe that the IEEE 1459 standard could be more useful for my case. Based on this standard, what values would the ION 7400 take into account and would it consider harmonics up to the 63rd order?

 

I appreciate your time in advance and look forward to your prompt response.

 

Sincerely,

Juan Quintanilla

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-06-20 09:54 AM

0 Likes
3
3385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-20 09:54 AM

Hello @JhimmyJMQT1 ,

 

Curious if the IEC62052-11 ed.2 §9.4.2.2 , §9.4.2.3 and §9.4.2.4  will meet the need.  ION7400 meets the Class 0,2S requirements.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
JhimmyJMQT1
JhimmyJMQT1
Explorer

Posted: ‎2024-06-25 01:53 PM

0 Likes
2
3343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-25 01:53 PM

Hello @Charles_Murison ,

 

And that about the IEEE 1459 ?, Can the ION7400 accurately measure power and energy parameters under harmonic distortions up to the 63rd order while adhering to the IEEE 1459 standard?

 

Understanding the capabilities of the ION7400 in this context would be very helpful. Any information or resources you can provide would be greatly appreciated.

 

Thank you for your time and assistance.

 

Sincerely,

Juan Quintanilla

Reply
Maaz
Maaz Explorer
Explorer

Posted: ‎2024-10-08 03:45 PM

0 Likes
0
3122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-08 03:45 PM

Hi @JhimmyJMQT1 ,

 

IEEE 1459-2010 is currently in the state of inactive-reserve and is being revised in a new standards project. The new edition is being balloted now. Schneider Electric is following the development of that new edition, which is focused on the fundamentals of how to compute kW and kVA under all conditions: balanced/unbalanced and sinusoidal/nonsinusoidal.

Reply
WillW
WillW
Explorer

Posted: ‎2024-10-08 10:08 PM

0 Likes
0
3108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-08 10:08 PM

The ION7400's 63rd harmonic measurement might be necessary for power quality.

Reply
DanL
DanL Champion
Champion

Posted: ‎2024-10-10 09:00 AM . Last Modified: ‎2024-10-10 09:01 AM

0 Likes
0
3095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-10 09:00 AM

Yes for the most part, the ION7400 provides quantities following the IEEE 1459 recommended algorithms for power. Some of the 1459 definitions are not provided by default, but the ION7400 can be easily configured to provide most of those. Was there a specific calculation or definition you are interested in?

The Power Meter module performs time domain calculations using 512 samples per (fundamental) cycle.

The Power Harmonics module performs frequency domain calculations up to the 63rd harmonic.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore