Hello @EdwardLSK ,
There could be a few different areas of investigation. First, does your meter have COMTRADE enabled? Second, does your meter have sag/swell enabled? Third, has your meter had a sag or swell event? Have you tried using manual waveform trigger?
The waveform viewer in the web is not a real time viewer, it will only look at waveforms stored in COMTRADE that have been triggered. Trigger can be from sag/swell module or manual waveform trigger.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @EdwardLSK ,
There could be a few different areas of investigation. First, does your meter have COMTRADE enabled? Second, does your meter have sag/swell enabled? Third, has your meter had a sag or swell event? Have you tried using manual waveform trigger?
The waveform viewer in the web is not a real time viewer, it will only look at waveforms stored in COMTRADE that have been triggered. Trigger can be from sag/swell module or manual waveform trigger.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @EdwardLSK
As Charles mentioned, here are the settings that need to be double-checked:
Best Regards,
-Mehran
L3 Expert Advanced metering