Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi Expertise,
I have PM5560 installed with
- wiring system 3Ph4Wye Grounded
- VT = 3 VTs 13800/110
- CT = 3 CTs 5000/1
PM not showing MVAr value since PF reading is 1.
Customers have comparison with another metering that showing MVAr value with PF reading is 0.99
I don't know is that any change to have more accuracy in PF may be?
I attach Phasor Diagram that capture from PM5560.
Link copied. Please paste this link to share this article on your social media post.
Hi @ahmaddedi,
Do you know the firmware version of the meters that show and do not show the reactive power, for comparison?
Please note that a power factor rounding issue was fixed in firmware version 4.4.0:
Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hi @ahmaddedi,
Do you know the firmware version of the meters that show and do not show the reactive power, for comparison?
Please note that a power factor rounding issue was fixed in firmware version 4.4.0:
Regards,
JD