Hi all,
Is it possible to use A9MEM1570 (3P + N) as a substitute for A9MEM15703 (3P) with neutral not connected? - Any feedback is appreciated.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hi @Patrick_Grehan,
Yes, this will fall under the first case: when the neutral is not connected (on load and PowerTag), the data by phase will be incorrect if the phases are not well balanced, but the total power/energies will be accurate.
Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hi @Patrick_Grehan ,
Without information about the location and installation of the PowerTag (PTag) and assuming it is a 3P +N system, we can make the following observations:
Best Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hi @Jesus_Diaz
Thanks for your response - to clarify, my question was around using the PTag on a 3P load (no neutral). Installing the 3P+N PowerTag (A9MEM1570) without the neutral connected, as per your comment above, may see some inaccuracy in phase data (if unbalanced) but overall power / energy data will be accurate. Have I summarised your response accurately?
Thanks,
PG
Link copied. Please paste this link to share this article on your social media post.
Hi @Patrick_Grehan,
Yes, this will fall under the first case: when the neutral is not connected (on load and PowerTag), the data by phase will be incorrect if the phases are not well balanced, but the total power/energies will be accurate.
Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hello @Patrick_Grehan ,
What are you going to do with the Neutral connector of your PowerTag F63 ?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hi Romain,
The neutral would not be connected and insulated. My question is basically if it's appropriate to do this.
Thanks,
PG