We have 1 DB on a site of 20 plus DB's that the meter is not converting the amps/volts into KWH correctly. It is a split metered DB with 2No A9MEE3255 installed. We are only getting recorded values of a few kilowatts when it should be a lot more. We have changed the meter for new one and checked all the wiring but can't see any issue. I am out of ideas if anyone can help
- Labels:
-
PowerTag Energy
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello,
What type of load are you using?
I suggest contacting your local support as we may need more information to provide you with a better answer.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Jesus_Diaz ,
Do you have any idea for should customer reach out to local technical support?
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Problem solved. It turned out to be the top (Lighting) section of the split load DB voltage connections had been connected wrong (V1-V3-V2) in the factory and this was causing the meter to read incorrectly. Swoped cable around to V1-V2-V3 and meter began to record correctly.