Power Factor
Metering & Power Quality
Select a Country
  • EcoStruxure Power & Grid
  • Power Factor
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
huynhngochoi
huynhngochoi
Explorer
Posted: ‎2024-07-24 05:03 AM
1613
Power Factor
I am using the PM8000 meter and encountering the following issue. The total Apparent Power of the 3 phases is 118.67, but the meter displays 105.789. Similarly, Active Power and Reactive Power are also displaying inaccuracies. Does anyone know why this is happening?
Thank you.
  • ION8000
Charles_Murison
Champion
Posted: ‎2024-07-24 08:09 AM
1
1595
Hello @huynhngochoi
Given the numbers you are seeing the numbers reported by the meter look correct to me.
In the ION meters there is 2 methods for calculating kVA,
Vector Sum or Scaler Sum, Vector Sum you can think of as using the total kW and KVAR to get kVA. Scaler Sum you can thank of as adding individual phases. Math may not be exactly that but close enough approximation.
Total
kW: 35.855 + 34.825 + 34.763 = 105.443
kVAR: -2.797 -2.757-2.994 = -8.548
kVA: (105.443^2+(-8.548(^2)^0.5 = 105.788
105.433/105.789 = 99.66%
Phase A
35.855/40.383 = 88.7873
repeat for phase B and C the number match the diagram.
Charles
Charles_Murison
Champion
1
1596
Hello @huynhngochoi
Total
Phase A
Charles
huynhngochoi
huynhngochoi
Explorer
Posted: ‎2024-07-24 08:21 AM
Thanks for your support.