PM8240 - TNS without a 4th current transformer

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8240 - TNS without a 4th current transformer
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2017-12-20 12:41 AM

0 Likes
5
2043
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-12-20 12:41 AM

PM8240 - TNS without a 4th current transformer

Hi,

The net is TNS. So we choose 4W-Wye in the setup of the PM8240.

But there isn't a current transformer placed on the Neutral.

Now we see for I5 (ground?) 40A and for I4 (Neutral) 0A. But I4 should be around 40A.

The Compact NSX, placed upstream of the PM8240, shows around 40A for the Neutral.

1. How to wire the I4 terminals when we do not have a current transformer?

Like shown on screenshot 1A or like shown on screenshot 1B? Or is this not so important?

2. Where to tell the PM8240 that a fourth current transformer is not present and that it should calculate the Neutral? (This is possible with a PM5560.)

Thanks!

BR,

Philippe

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2018-02-09 02:00 PM

3 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-09 02:00 PM

If you have only 3CTs for a 3 phase system (with either 3 or 4 wires), you should use the "3CT" wiring diagram.

Ideally, one of the I4 terminals should be jumpered to the grounded CT common, but it should also work fine if I4 is not connected.

The "I5" measurement on the PM8240 is the calculated residual current of I1 + I2 + I3 + I4. So when I4 is not used (as shown above) and you have a 4wire system, this should be the neutral current.

If the I5 measurement is not your expected neutral current, you may have have a CT polarity, phase swap, or ground fault issue.

I recommend do NOT simply connect I4+ to I4- as it can become a loop antenna that may allow the meter to register when in close proximity to AC magnetic fields.

See Answer In Context

Reply
Replies 5
Yut
Captain Yut
Captain

Posted: ‎2017-12-21 08:55 PM

0 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-12-21 08:55 PM

Just simply connect I4+ and I4- together.

Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2018-02-09 02:00 PM

3 Likes
0
2001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-09 02:00 PM

If you have only 3CTs for a 3 phase system (with either 3 or 4 wires), you should use the "3CT" wiring diagram.

Ideally, one of the I4 terminals should be jumpered to the grounded CT common, but it should also work fine if I4 is not connected.

The "I5" measurement on the PM8240 is the calculated residual current of I1 + I2 + I3 + I4. So when I4 is not used (as shown above) and you have a 4wire system, this should be the neutral current.

If the I5 measurement is not your expected neutral current, you may have have a CT polarity, phase swap, or ground fault issue.

I recommend do NOT simply connect I4+ to I4- as it can become a loop antenna that may allow the meter to register when in close proximity to AC magnetic fields.

Reply
Mannguyen
Lieutenant | EcoXpert Master Mannguyen Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-07-17 10:05 PM

0 Likes
2
860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-17 10:05 PM

I agreed with the remaining question from @Philippe_Morel and somebody may help me with this:

''2. Where to tell the PM8240 that a fourth current transformer is not present and that it should calculate the Neutral? (This is possible with a PM5560.)''. Thank you in advance.

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-07-19 08:51 AM

0 Likes
0
814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-19 08:51 AM

Hello @Mannguyen ,

 

There is not way to tell the PM8000 meters that there is not 4th CT. Have a look at https://www.se.com/ca/en/faqs/FAQ000232697/ for more information on wiring options.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2024-07-19 10:26 AM

1 Like
0
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-19 10:26 AM

The PM8240 will always both measure I4 and also calculate the residual of all measured inputs.

When you have only 3CTs directly connected to the meter's I1, I2, and I3 inputs:
- the residual is the Neutral current for a 4wire system (assuming no ground faults)

- the residual is the Ground current for a 3wire system

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of