If several meters of reference A9MEM3350 are throwing errors 203/204 which are being used in photovoltaic systems. It is understandable, that this problem is caused by a wiring issue and phase sequence issue. *(Assume no config, phase and wiring issue)
Lets say these meters are not 4 quadrant meters, so they would not be measuring imported-exported energy. Is it a suitable choice then in a sense that it would work in this kind of setup (photovoltaic generation) at all or no and might be causing these errors?
Will these two errors (203/204) could be caused by the fact that sometimes the current might be circulating backwards on the CT, due to the photovoltaic production and causing these errors?
I will really appreciate any comments in this matter to clear up these doubts.
Thank You!
Yours,
AK
Link copied. Please paste this link to share this article on your social media post.
Hello @Asif_Khan ,
203 - phase sequence reversed is only a voltage thing, the phase angle of current does not apply.
204 - Yes if current is flowing from load to line, yes you would see this error code.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Asif_Khan ,
203 - phase sequence reversed is only a voltage thing, the phase angle of current does not apply.
204 - Yes if current is flowing from load to line, yes you would see this error code.
Regards,
Charles