PM8000 control on NSX Circuit Breakers

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 control on NSX Circuit Breakers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Arneil_Dalope
Lt. Commander | EcoXpert Master Arneil_Dalope Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2020-12-13 03:10 PM

0 Likes
3
2279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-13 03:10 PM

PM8000 control on NSX Circuit Breakers

Hi,

 

We would like to control the NSX circuit breakers as Modbus slaves from a PM8000.

 

Any advise/gotchas in this setup? 

 

Thank you.

 

Regards,
Arneil

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2020-12-13 11:59 PM . Last Modified: ‎2020-12-14 12:00 AM

1 Like
0
2273
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-13 11:59 PM

Hello @Arneil_Dalope , 

 

I have a similar configuration in my Lab that is working fine. I use a ION9000 but it will be the same for PM8000.

 

Just ensure that you have set up you ION meter as a "Modbus Master". You can check this by the web page or ION Setup. 

 

0IONSetup_Serial_Settings.png

 

If you connect your system to EPC : All IFMs slaves connected to the ION Meters will be discovered.

 

EPC_ION9K_Gateway.png

 

Please check also the serial settings of your IFMs. Modbus SL Auto Link Adapt can be activated.

 

EPC_ION9K_IFMs.png

 

From this point : you will be able to send write command to the NSX.


Regards, 

 

Romain

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-12-14 09:05 AM

2 Likes
0
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-14 09:05 AM

Hello @Arneil_Dalope , 

 

One addition to what Romain said is that the PM8000 needs to have the modbus gateway function enabled. This can be found in the Modbus Master Options module. You will want to configure the serial connection 1 to Com1, then enable the gateway to Serial connection 1.

 

If you are asking about having the PM8000 send the series of commands to the breaker without software, this would not work. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2020-12-13 11:59 PM . Last Modified: ‎2020-12-14 12:00 AM

1 Like
0
2274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-13 11:59 PM

Hello @Arneil_Dalope , 

 

I have a similar configuration in my Lab that is working fine. I use a ION9000 but it will be the same for PM8000.

 

Just ensure that you have set up you ION meter as a "Modbus Master". You can check this by the web page or ION Setup. 

 

0IONSetup_Serial_Settings.png

 

If you connect your system to EPC : All IFMs slaves connected to the ION Meters will be discovered.

 

EPC_ION9K_Gateway.png

 

Please check also the serial settings of your IFMs. Modbus SL Auto Link Adapt can be activated.

 

EPC_ION9K_IFMs.png

 

From this point : you will be able to send write command to the NSX.


Regards, 

 

Romain

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-12-14 09:05 AM

2 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-14 09:05 AM

Hello @Arneil_Dalope , 

 

One addition to what Romain said is that the PM8000 needs to have the modbus gateway function enabled. This can be found in the Modbus Master Options module. You will want to configure the serial connection 1 to Com1, then enable the gateway to Serial connection 1.

 

If you are asking about having the PM8000 send the series of commands to the breaker without software, this would not work. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Yut
Captain Yut
Captain

Posted: ‎2020-12-16 11:27 PM

0 Likes
0
2256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-16 11:27 PM

I have just do something similar sending kW reading to big LED display using Modbus from the ION7400. 

You need to set com1 to Modbus Master protocol then use Modbus Export module sending data.

 

If you want to write something to Modbus device be you have disable reading. If the Modbus Master module are used it need to be disable prior to write. The pending logic of the Modbus Export Module plus And/Or Module to disable/enable the Modbus Master module. 

 

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of