Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 MV wiring

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 MV wiring
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Szymon_Hochół
Szymon_Hochół Champion
Champion

Posted: ‎2020-10-28 04:19 AM

0 Likes
8
5381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-28 04:19 AM

ION9000 MV wiring

Hello Experts,

I am looking for some guidance in wiring and configuring ION9000 in MV network.

The system is 6kV DELTA, and the switchboard has 3 voltage transformers. They are connected like this:

Przechwytywanie2.JPG

However, for a DELTA system, ION9000 installation manual does not include such setup. It presents direct connection or using two VTs:

Przechwytywanie.JPG

How would you wire and configure (volts mode, nominal voltage etc.) the meter in such case? 

 

Thank you in advance.

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
DanL Champion
Champion

Posted: ‎2020-11-02 10:08 AM

0 Likes
2
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-02 10:08 AM

nominal voltage that should be configured:
4W-WYE use L-N rms Primary voltage as nominal (which in your case is line-to-earth because that is how the PT primaries are wired)
DELTA use L-L rms Primary voltage

The "Vnominal" setup register in the Factory module in ION9000 default template/framework is linked to the input of many other modules. Right+click on the register and select "Show Connections"

 

 

If you use the DELTA volts mode, and the connection that you described, you could leave VN, VE, V4 not wired at all, but we recommend connecting those terminals as indicated on the drawing. If possible, you should use the fourth wire from PTs (which is ground). That makes the wiring the same as for 4W-WYE, and you can switch over at a later point if you wish to measure line-to-earth voltages (using the meter's VLN output registers in 4WYE mode).

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 8
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-10-29 09:12 AM

0 Likes
0
5373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-29 09:12 AM

Hello @Szymon_Hochół ,

 

I will want to confirm with an engineer, will let you know.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
DanL Champion
Champion

Posted: ‎2020-10-29 04:19 PM

1 Like
6
5367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-29 04:19 PM

 

The secondary of the 3PTs are connected together and form a COMMON potential and a 4th wire for voltage.
The PT SECONDARY wiring always determines the volts mode used with ION meters.
 
There are two good options:
Use 4W-WYE volts mode and connect meter's VN measurement terminal to ground (the PT common). The meter's line-to-neutral registers will report the system line-to-ground voltage. Line-to-line voltages will reflect system line-to-line voltages (of course)
OR
Use DELTA volts mode and connect only V1, V2 and V3 measurement terminals (just like a "3 wire direct delta connection" to the PT secondary). Now the meter will only report line-to-line system voltages.
 
Tags (1)
  • Tags:
  • english
Reply
Szymon_Hochół
Szymon_Hochół Champion
Champion

Posted: ‎2020-10-30 12:33 AM

0 Likes
5
5360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-30 12:33 AM

Thank you @DanL.

 

There is another thing that's not clear for me: choosing volts mode affects the nominal voltage that I should configure. With 4W-WYE, I should use L-N voltage as nominal (which is not there, because there is no N), with 3W-DELTA I should use L-L voltage. This parameter will affect sag/swell detection and harmonics calculations, according to meter's user manual. So woudn't the use of 4W-WYE result in some wrong calculations?

 

And one last thing, If I use the DELTA mode, and connection that you described - can we leave VN, VE, V4 be not wired at all?  Or should we ground it as indicated on the drawing? If these need to be grounded, why not use the fourth wire from PTs (which is ground)? But that makes the wiring the same as for 4W-WYE. Or am I wrong?

 

Thanks

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-10-30 02:47 PM

0 Likes
0
5353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-30 02:47 PM

Hello @Szymon_Hochół,

 

It is possible to configure the meter to use VLL information only. Some of the changes are just a setup register (like with sag/swell module) other changes may be linking the LL input rather than LN. If you want to explorer this more I would recommend contacting technical support.

 

Regarding the wiring I would have to defer to Dan.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
DanL Champion
Champion

Posted: ‎2020-11-02 10:08 AM

0 Likes
2
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-02 10:08 AM

nominal voltage that should be configured:
4W-WYE use L-N rms Primary voltage as nominal (which in your case is line-to-earth because that is how the PT primaries are wired)
DELTA use L-L rms Primary voltage

The "Vnominal" setup register in the Factory module in ION9000 default template/framework is linked to the input of many other modules. Right+click on the register and select "Show Connections"

 

 

If you use the DELTA volts mode, and the connection that you described, you could leave VN, VE, V4 not wired at all, but we recommend connecting those terminals as indicated on the drawing. If possible, you should use the fourth wire from PTs (which is ground). That makes the wiring the same as for 4W-WYE, and you can switch over at a later point if you wish to measure line-to-earth voltages (using the meter's VLN output registers in 4WYE mode).

Tags (1)
  • Tags:
  • english
Reply
Szymon_Hochół
Szymon_Hochół Champion
Champion

Posted: ‎2020-11-03 01:11 AM

0 Likes
0
5339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-03 01:11 AM

Thank you for your support @DanL , @Charles_Murison .

I'll let you know how it works once we get to install the meter.

 

Have a good day!

Tags (1)
  • Tags:
  • english
Reply
conradvr_hexeis
conradvr_hexeis
Contributor

Posted: ‎2020-12-20 08:17 PM

1 Like
0
5326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-20 08:17 PM

Hi @DanL,

 

This is similar to an issue Hexeis have a few years ago with the ION7650 used on 3W Delta Networks with Star-Star PT installations.  Over the last 10 years Hexeis has never had an ION installation in Australia that uses the PT arrangement as shown in the installation sheet.  Most of the PT installations are used for Protection relays hence the Star-Star design.

 

Hexeis consulted with Schneider technical support at the time and the information received noted (original case number 1381097).

 

The feedback received at the time was using Delta mode results in measuring voltages across 2 PT windings instead of 1 so this impacts accuracy.  I also recall some chat about the effect of the phase shift caused by the PTs.

 

Since then Hexeis has always used the Volts Mode 4W-WYE and adjusted the Nominal Voltages etc to suit.

 

It would be very useful to have a factory document that displayed the alternative wiring diagrams, provided recommended configurations and noted the impact on accuracy and other metering performance.  Can this please be provided?

 

Regards,

Conrad

Tags (1)
  • Tags:
  • english
Reply
conradvr_hexeis
conradvr_hexeis
Contributor

Posted: ‎2020-12-20 08:44 PM

2 Likes
0
5324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-20 08:44 PM

Hi @Szymon_Hochół 

 

With the Sag/Swell module you can also use the Setup Register "Use Vll Always" to use V line to line voltages even when their are line to neutral (earth) voltages available i.e. when using 4W-WYE.

 

Regards,

Conrad

Hexeis 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore