PM8000 Waveform explanation

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Waveform explanation
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Koen_Rowies
Lt. Commander Koen_Rowies Lt. Commander
Lt. Commander

Posted: ‎2018-03-13 08:02 AM

2 Likes
7
2448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 08:02 AM

PM8000 Waveform explanation


Hello,

I have some questions about some PM8000 devices that have captured some waveforms.

First PM8000 supplies feeds a cabinet with isolation transformers (hospital operation rooms).

The PM8000 captured some some strange waveforms. It's like the neutral point has suddenly shifted...

Customer had no complaints of interruptions or distortions from the users... There a several PM8000 devices on site and only on this device we captured this kind of distortions.... Is there anybody who has seen similar captures or could explain what happened? Could this be a problem on the PM8000 meter?

Second capture is about power interruptions. As the PM8000 Auxiliary supply is not on UPS power. When we lose power, I guess the PM8000 can make a last capture with the energy stored in the internal capacity of the PM. But when the power comes back it's not possible because the meter is off and it takes some time to boot... However, we captured these waveforms... I would to see a capture where voltage and current drops but this is what we see... Can someone explain what we see here?

Reports can be downloaded from box: https://schneider-electric.box.com/s/dhgl28nuey0lsberp3y828xg3t08nisz

Maybe it would be interesting to make a place on the exchange to share some waveforms with information about incidents. There is not so much information available about these things...

Br,

Koen

Tags (4)
  • Tags:
  • pm8000
  • waveform analysis
  • waveform_distortion
  • waveforms
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2018-03-15 01:54 PM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-15 01:54 PM

Hi Koen,

Please contact your local TSC center which is located in Prague and they will escalate to the expert support center as needed. Below is their email address: aut.csc@cz.schneider-electric.com

Thanks

Leo

Jozef GAAL​

See Answer In Context

Reply
Replies 7
Anonymous user
Not applicable

Posted: ‎2018-03-15 01:54 PM

0 Likes
0
2345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-15 01:54 PM

Hi Koen,

Please contact your local TSC center which is located in Prague and they will escalate to the expert support center as needed. Below is their email address: aut.csc@cz.schneider-electric.com

Thanks

Leo

Jozef GAAL​

Reply
sesa37232_bridg
Crewman sesa37232_bridg Crewman
Crewman

Posted: ‎2018-03-16 02:10 PM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-16 02:10 PM

The first waveform appears as if the power source has a resistance grounded neutral or an ungrounded neutral. A ground fault on one of the phases will not cause high current flow but it will raise the neutral voltage value to be approximately the Line to Neutral voltage above 0 volts. If the ground fault is momentary the neutral voltage will slowly decay to be at 0 volts again.

Reply
Yut
Captain Yut
Captain

Posted: ‎2018-03-19 09:47 PM

0 Likes
1
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-19 09:47 PM

The first two look like there is negative DC bias into power line I saw something similar quite often in the 115 kV line when there was lightning strike near the line.

Reply
Koen_Rowies
Lt. Commander Koen_Rowies Lt. Commander
Lt. Commander

Posted: ‎2018-03-20 01:15 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-20 01:15 AM

The PM8000 is in a TNS electrical network and powers some isolation transformers IT . They are also equiped with some insulation monitoring devices from Bender.

Reply
Koen_Rowies
Lt. Commander Koen_Rowies Lt. Commander
Lt. Commander

Posted: ‎2018-03-29 06:15 AM

0 Likes
1
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-29 06:15 AM

Hello,

After properly checking the information L4 replied saying that, this is expected behavior of an isolated IT system during (and recovering from) a single line fault.

The second waveform, I could reproduce in our lab and is due to voltage interruption on the aux and voltage inputs. But i have no explanation what this just shows... Customer will put the auxilary power on UPS.

Br,

Koen

Reply
greg_expoenergy
Lt. Commander greg_expoenergy
Lt. Commander

Posted: ‎2018-07-21 02:22 PM

1 Like
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-21 02:22 PM

This will typically happen if one loses the input supply and one has motors running as loads. In this case the supply voltage will go to zero and what you are seeing is the back-emf of the motors as they run down and demagnetize. They regenerate into the supply and dissipate all electrical energy stored within them.

That is generally why one should wait until all transients have died down before switching back in as one can create large motor transient current and torque if one switches the mains back in and out of sync with the back-emf's.

Reply
greg_expoenergy
Lt. Commander greg_expoenergy
Lt. Commander

Posted: ‎2018-07-21 02:27 PM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-21 02:27 PM

This is quite normal and common and depends on the type of downstream or upstream fault which is normally due to an unsymmetrical type fault. It depends on the point at which the fault occurs as well as the nature of the unsymmetrical fault.

see

https://relaytraining.com/what-is-dc-offset-ask-chris/

https://myelectrical.com/notes/entryid/134/dc-component-of-asymmetrical-faults

http://www.nptel.ac.in/courses/117104071/chap6.pdf

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of