Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82463members
350020posts

PM8000 Waveform explanation

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Koen_Rowies
Lt. Commander Lt. Commander
Lt. Commander

PM8000 Waveform explanation


Hello,

I have some questions about some PM8000 devices that have captured some waveforms.

First PM8000 supplies feeds a cabinet with isolation transformers (hospital operation rooms).

The PM8000 captured some some strange waveforms. It's like the neutral point has suddenly shifted...

Customer had no complaints of interruptions or distortions from the users... There a several PM8000 devices on site and only on this device we captured this kind of distortions.... Is there anybody who has seen similar captures or could explain what happened? Could this be a problem on the PM8000 meter?

Second capture is about power interruptions. As the PM8000 Auxiliary supply is not on UPS power. When we lose power, I guess the PM8000 can make a last capture with the energy stored in the internal capacity of the PM. But when the power comes back it's not possible because the meter is off and it takes some time to boot... However, we captured these waveforms... I would to see a capture where voltage and current drops but this is what we see... Can someone explain what we see here?

Reports can be downloaded from box: https://schneider-electric.box.com/s/dhgl28nuey0lsberp3y828xg3t08nisz

Maybe it would be interesting to make a place on the exchange to share some waveforms with information about incidents. There is not so much information available about these things...

Br,

Koen


Accepted Solutions
ChenLiang
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
900

Re: PM8000 Waveform explanation

Hi Koen,

Please contact your local TSC center which is located in Prague and they will escalate to the expert support center as needed. Below is their email address: aut.csc@cz.schneider-electric.com

Thanks

Leo

Jozef GAAL

See Answer In Context

7 Replies 7
ChenLiang
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
901

Re: PM8000 Waveform explanation

Hi Koen,

Please contact your local TSC center which is located in Prague and they will escalate to the expert support center as needed. Below is their email address: aut.csc@cz.schneider-electric.com

Thanks

Leo

Jozef GAAL

sesa37232_bridg
Crewman Crewman
Crewman
0 Likes
0
900

Re: PM8000 Waveform explanation

The first waveform appears as if the power source has a resistance grounded neutral or an ungrounded neutral. A ground fault on one of the phases will not cause high current flow but it will raise the neutral voltage value to be approximately the Line to Neutral voltage above 0 volts. If the ground fault is momentary the neutral voltage will slowly decay to be at 0 volts again.

Yut
Captain
Captain
0 Likes
1
900

Re: PM8000 Waveform explanation

The first two look like there is negative DC bias into power line I saw something similar quite often in the 115 kV line when there was lightning strike near the line.

Koen_Rowies
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
900

Re: PM8000 Waveform explanation

The PM8000 is in a TNS electrical network and powers some isolation transformers IT . They are also equiped with some insulation monitoring devices from Bender.

Koen_Rowies
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
900

Re: PM8000 Waveform explanation

Hello,

After properly checking the information L4 replied saying that, this is expected behavior of an isolated IT system during (and recovering from) a single line fault.

The second waveform, I could reproduce in our lab and is due to voltage interruption on the aux and voltage inputs. But i have no explanation what this just shows... Customer will put the auxilary power on UPS.

Br,

Koen

greg_expoenergy
Lt. Commander
Lt. Commander

Re: PM8000 Waveform explanation

This will typically happen if one loses the input supply and one has motors running as loads. In this case the supply voltage will go to zero and what you are seeing is the back-emf of the motors as they run down and demagnetize. They regenerate into the supply and dissipate all electrical energy stored within them.

That is generally why one should wait until all transients have died down before switching back in as one can create large motor transient current and torque if one switches the mains back in and out of sync with the back-emf's.

greg_expoenergy
Lt. Commander
Lt. Commander
0 Likes
0
900

Re: PM8000 Waveform explanation

This is quite normal and common and depends on the type of downstream or upstream fault which is normally due to an unsymmetrical type fault. It depends on the point at which the fault occurs as well as the nature of the unsymmetrical fault.

see

https://relaytraining.com/what-is-dc-offset-ask-chris/

https://myelectrical.com/notes/entryid/134/dc-component-of-asymmetrical-faults

http://www.nptel.ac.in/courses/117104071/chap6.pdf