Alarms PM5560

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Alarms PM5560
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
489
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
90
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2017-10-09 07:04 AM . Last Modified: ‎2020-04-22 01:10 AM

0 Likes
3
1084
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-10-09 07:04 AM

Alarms PM5560

Dear,

 

I have problems configuring alarms on a PM5560 with ION Setup.

 

I can configure the alarms on the device or with Vista (PME), so the PM5560 does work.

 

This is the version of ION Setup:

I believe it is the latest version

 

This is the version of the meter:

I believe it is the latest version.

 

I could once configure an alarm through ION Setup. But now it is not possible anymore because ION Setup gives the values multiplied by 1000 (e.g. 20A is read as 20000A).

 

I can now only change the Pickup Limit and Enable through ION Setup.

 

Can this be fixed?

 

Thanks!

 

BR,

Philippe

Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2017-10-30 09:24 AM

0 Likes
2
1043
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-10-30 09:24 AM

Hi Philippe,

I used ION Setup to program a PM5563 Over Current alarm and had no problems.  I'm very surprised that you were able to use PME to program the alarms since its a very complex operation on the device and PME technically doesn't know how to program Modbus-based devices (especially ones which are not read/write of direct registers).  Programming of the PM556x alarms via the front panel restricts the use of non-integer values for the limits as you can only enter integer values from the front panel display (ex. Programming a limit of 12.345 via ION Setup will only display 12 on the front panel screen when viewed, and attempting to program that alarm for any reason will then reset the limit to 12.000).

Pay attention to the status bar when attempting to program the values as it might be indicating that both limits are out of range (limits are restricted based on the PT/CT ratios), so you may need to temporarily alter the ratios, modify the limits to a smaller values and then alter the PTs/CTs back to normal.  If this is the case, let me know and I'll look into how we could maybe resolve this issue going forward (it is difficult in that if there are multiple settings, allow you to move away from that screen causes other issues).

Reply
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2017-11-02 01:04 AM

0 Likes
1
1043
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-11-02 01:04 AM

Hi Robert,

Thank you for testing it.

I'll look into it and let you know how it goes.

I  can confirm that programming the PM5560 alarms works well with PME (VISTA).

But on the other end it is not possible to program a "logic" alarm (and, or,..).

Reply
michael_stith_g
Lieutenant | EcoXpert Master michael_stith_g Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2018-07-24 10:52 AM

0 Likes
0
1043
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-24 10:52 AM

Phillipe,

There is a newer frimware for the PM5560 meter that may also help.  Latest Firmware is 2.4.3    https://www.schneider-electric.co.uk/en/download/search/Firmware%20PM5560_PM5563%20Version%202.4.3/

Respectfully,

Michael Stith
Albireo Energy
6525 The Corners Parkway
Suite 102
Peachtree Corners, Georgia 30092-3349
Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of