PM8000 Vx-Dip YZ Modbus Registers

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Vx-Dip YZ Modbus Registers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
525
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
dsantillan
Lieutenant dsantillan
Lieutenant

Posted: ‎2023-06-02 02:04 PM

0 Likes
2
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-02 02:04 PM

PM8000 Vx-Dip YZ Modbus Registers

Hello, 

 

Upon review of the modbus mapping for PM8000 I found registers from 40246 to 40344 and their counters on registers 40546 to 40644.

 

Is there a document explaining what each of these registers hold? 

 

Thank you, 

Attachments
Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-06-02 04:23 PM

0 Likes
1
1317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-02 04:23 PM

Hello @dsantillan ,

 

A bit of a loaded question. The registers you are highlighting are link to modbus via a Data mapping Module "Data Mapping EN 1". The default framework does not have any registers linked by default. The intention for these registers is if a Bin module is linked. In the setup of the Bin module, there are 1 to 25 rules that determine when evaluate is pulse, what Bin output needs to be incremented. 

 

Likely something similar for V1-Intrpt N1, possible to link a Bin module however not linked by default.

 

An example of where a Bin module is used is for EN50160, voltage dip. The Bin module has 2 inputs, the SS min magnitude, and SS duration. If magnitude is greater or equal to 80 and greater or equal to 90 and the duration is less than 0.2. Bin 1 (V-Dip A1) is incremented. 

 

For more information on the Bin module refer to ION reference (https://www.productinfo.schneider-electric.com/pm8000/595e26f146e0fb0001f6ffc4/IONReference/English/...)

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-06-02 04:23 PM

0 Likes
1
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-02 04:23 PM

Hello @dsantillan ,

 

A bit of a loaded question. The registers you are highlighting are link to modbus via a Data mapping Module "Data Mapping EN 1". The default framework does not have any registers linked by default. The intention for these registers is if a Bin module is linked. In the setup of the Bin module, there are 1 to 25 rules that determine when evaluate is pulse, what Bin output needs to be incremented. 

 

Likely something similar for V1-Intrpt N1, possible to link a Bin module however not linked by default.

 

An example of where a Bin module is used is for EN50160, voltage dip. The Bin module has 2 inputs, the SS min magnitude, and SS duration. If magnitude is greater or equal to 80 and greater or equal to 90 and the duration is less than 0.2. Bin 1 (V-Dip A1) is incremented. 

 

For more information on the Bin module refer to ION reference (https://www.productinfo.schneider-electric.com/pm8000/595e26f146e0fb0001f6ffc4/IONReference/English/...)

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
dsantillan
Lieutenant dsantillan
Lieutenant

Posted: ‎2023-06-02 04:42 PM

0 Likes
0
1315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-02 04:42 PM

Hello Charles, 

 

Thank you for the great input. I think I got it. 

 

The first thing is to set the module and then, based on that configuration the commissioned registers will start counting as per the applied definitions and be reflected on those modbus registers. 

 

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore