Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @huseyinb ,
Until this is fixed in V3.2, you can use V3.1 version of ION Setup.
Link copied. Please paste this link to share this article on your social media post.
If you set the meter to advanced configuration can you open the modbus slave modules? Are these modules offline? Are the inputs linked to this/these module(s)? If not, does linking the inputs allow the module to be online?
Link copied. Please paste this link to share this article on your social media post.
I believe that particular setup wizard in ION Setup is only for user created/customized Modbus registers (via Modbus Slave modules).
I think the customer might be looking for the default Modbus register list for the PM8000 (available on the web)?
Link copied. Please paste this link to share this article on your social media post.
Thanks, but customer has a lot of arithmetic modules, they need modbus register address for these modules,
Link copied. Please paste this link to share this article on your social media post.
Hello @huseyinb ,
Until this is fixed in V3.2, you can use V3.1 version of ION Setup.
Link copied. Please paste this link to share this article on your social media post.
Hi Charles,
Can you share v3.1 setup?
Link copied. Please paste this link to share this article on your social media post.
Hi @huseyinb ,
I do not remember if there is a BOX link to find all release of ION Setup...
In any case, I enclose the release 3.1.19276.01 to this post.
Regards,
Romain
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @huseyinb ,
I have edited my post...
Enclosed file was a .exe (forbidden format). I have zipped the install file.
Regards,
Romain
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.