Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Currently the PM8000 and ION 7400 series meters have separate current and voltage nominal settings, but their respective waveform recorder module Enable inputs share the same 'Wfm Rec Enble' External Boolean status. A customer expressed interest in only recording voltage data because the loads being monitored are not constantly pulling current data causing a large number of unwanted waveform captures. We were able to assist by creating a custom External Boolean module, unlinking the 'Wfm Rec Enble' status, and linking the new custom module. Would it be possible to include the separation of current and voltage waveform capture in the default dcf template files in the future?
Link copied. Please paste this link to share this article on your social media post.
I'd like clarification on the "large number of unwanted waveform captures".
The question about Nominal Current is a separate topic, but as far as I know it is only used for the "Current Sag" and "Current Swell" framework features. The intent is that the customer would set it to some reasonable level of expected primary line current in Amps.
Posted: 2017-06-29 09:03 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Adam,
Really appreciate you sharing this type of insight and feedback. I'll leave it to Offer Management (Daniel Brandao Neto) to comment on the feature request.
Would it be possible for you to share your framework file that you developed to address the solution? It would be helpful to have for others if they come across a similar situation.
Thanks,
Adam
Link copied. Please paste this link to share this article on your social media post.
Hello,
I'm currently facing some difficulties to explain to our customer why should or why should him not set the nominal current in order to capture current waveform. I mean, as a matter of fact, current is a load dependent parameter and, therefore, it can vary from zero to the nominal value many times over the day. So, in order to help us to answer the customer questions, think about the solutions and applications, could you share with us what Development/Engineering teams thought of when inserted this possibility in newer versions of ION meters?
Thanks!
Kind regards,
Ramon
Link copied. Please paste this link to share this article on your social media post.
I'd like clarification on the "large number of unwanted waveform captures".
The question about Nominal Current is a separate topic, but as far as I know it is only used for the "Current Sag" and "Current Swell" framework features. The intent is that the customer would set it to some reasonable level of expected primary line current in Amps.
Link copied. Please paste this link to share this article on your social media post.
Hello Ramon,
An example I have seen where Current Sag/swell logic was used was a Data center where the loads where expected to be fairly consistent. The change in current would notify the user that something has changed with the system. Some times the changes would be expected and the alarm dismissed. However if not expected, the alarm would indicate a change that would require investigation.
Charles