PM8000 Power Factor as -1 and 1

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Power Factor as -1 and 1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
520
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
131
Ramasamy_N
Captain Ramasamy_N Captain
115
Robert_Lee
Admiral Robert_Lee Admiral
96
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Sushant_Belote
Lt. Commander | EcoXpert Master Sushant_Belote Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2025-09-15 12:59 AM . Last Modified: ‎2025-09-15 01:00 AM

0 Likes
3
231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-15 12:59 AM

PM8000 Power Factor as -1 and 1

Hi Team,

We are having 350+ PM8000 installed at site.
Currently If we see Power Factor on PME it shows in percentage (%).

As mentioned, in PM8000 manual we can have as -1 and 1 or as a percentage from -100% to 100%.

Power factor (PF) 

Sushant_Belote_0-1757922660841.png

I have tried searching for settings, but unable to find any.

I am aware of the process that opening framework in designer & adding extra modules to converter this to -1 to 1, but as meter quantity is huge it takes lots of time to configure for all meters.

May I know any better possible solution or some setting in ION setup?

 

Thanks & Regards

Sushant Belote

Labels
  • Labels:
  • ION Setup
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-09-16 09:57 AM

0 Likes
0
198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-16 09:57 AM

Hello @Sushant_Belote,

 

I did some digging and now understand where the comment is coming from. On the display of the PM8000 meter, PF is -1 to 1. The displays take readings from ION handles then divides by 100 in the display code. PME reads ION handles that are in % values. There is no setting inside the meter to switch how the ION handles are read.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-09-15 11:17 AM

0 Likes
0
213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-15 11:17 AM

Hello @Sushant_Belote ,

 

I am guessing you saw the post about setting from ION Reference. This document spans multiple ION meters and not all ION meters have the same settings or registers. For PM8000 meters, there is no way to change the PF value from percent to -1 to 1 as a setting. Given these are ION meters, it is possible to make a framelet that takes the PF reading and divides by 100. If you save this framelet in designer, you could then paste this framelet onto other meters in designer. Note that framelet is a piece of a temple, not entire meter's framework/template. In Designer, select the modules desired to be copied, and select edit -> Paste to framework.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Sushant_Belote
Lt. Commander | EcoXpert Master Sushant_Belote Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2025-09-15 09:24 PM

0 Likes
1
205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-15 09:24 PM

Hi @Charles_Murison 

I have seen this in PM8000 online guide, so I assume there must be some settings.

I have shared the link in original post also, sharing again.

Power factor (PF) 

I am aware the fact that creating framelet & pasting into each meter from designer, but I thought changing settings will be much easier, so I have posted.

 

Thanks & Regards

Sushant Belote

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-09-16 09:57 AM

0 Likes
0
199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-16 09:57 AM

Hello @Sushant_Belote,

 

I did some digging and now understand where the comment is coming from. On the display of the PM8000 meter, PF is -1 to 1. The displays take readings from ION handles then divides by 100 in the display code. PME reads ION handles that are in % values. There is no setting inside the meter to switch how the ION handles are read.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore