【PM8000】ION setup Phasor Viewer

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • 【PM8000】ION setup Phasor Viewer
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2024-05-22 01:59 AM

0 Likes
3
771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-22 01:59 AM

【PM8000】ION setup Phasor Viewer

Hello,

 

The PM8000 was set to delta and three-phase voltage was applied.

However, ION setup Phasor Viewer displays V32 180 degrees off.

 

Do you know why it appears like this?

The phasor is displayed properly in the web application.

Miyai_0-1716368294324.png

 

 

 

Regards,

Miyai

 

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-05-22 07:06 AM

2 Likes
0
748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-22 07:06 AM

Hi @Miyai 

In Delta systems, the phasor diagram shown in two different methods:
1- System view(120° Delta) which all 3 phases are shown. 120 degree between all 3 phases.
2- Instrument view(60° Delta) which only 2 phases are shown as yours. 60 degree between V12 and V32.

This view can be changed in ION Setup -> Tools -> Options -> Conventions -> Delta Vector Display: 

Mehran_Mehrnia_0-1716386073449.png

 



Best Regards,

-Mehran
L3 Expert Tech Support Specialist

See Answer In Context

Reply
Replies 3
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-05-22 07:06 AM

2 Likes
0
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-22 07:06 AM

Hi @Miyai 

In Delta systems, the phasor diagram shown in two different methods:
1- System view(120° Delta) which all 3 phases are shown. 120 degree between all 3 phases.
2- Instrument view(60° Delta) which only 2 phases are shown as yours. 60 degree between V12 and V32.

This view can be changed in ION Setup -> Tools -> Options -> Conventions -> Delta Vector Display: 

Mehran_Mehrnia_0-1716386073449.png

 



Best Regards,

-Mehran
L3 Expert Tech Support Specialist

Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-05-22 10:48 AM . Last Modified: ‎2024-05-22 11:07 AM

2 Likes
1
734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-22 10:48 AM

There are 2 different users that typically use ION Setup: Utility electricians who are wiring up the PTs/CTs using the phasors to confirm the wiring: They care what the vectors look like on the secondary side (instrumentation view) of the PT/CT and all other users who only care what the phasors look like on the primary side (or system view).

For instrumentation view, the vectors in a typical 2 wire Delta will have a 60 degree angle difference between Vab (or V12) versus Vcb (or V32).

In system view, the vector for Vbc is flipped 180 degrees so its down in quadrant 3 at 240 degrees typically so there's a 120 degree difference between the 2 phases as expected.

Mehran shows where you can adjust which of these 2 ION Setup use cases you wish to use with the default being for the utility electrician.

Reply
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2024-05-23 01:02 AM

0 Likes
0
712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-23 01:02 AM

Hi @Mehran_Mehrnia , @Robert_Lee 

 

Thanks for your advice.
I was able to see the phasor display.

 

 

Best regards,

Miyai

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of