New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
ION8650 Dynamic programming connection limitation
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2024-05-1501:20 PM
ION8650 Dynamic programming connection limitation
Hello SE experts,
The ION8650 meter supports a maximum of eight simultaneous Ethernet connections, however, I have dynamic programming site that more than 8 sub meters need to be connected to the modbus master meter.
Link copied. Please paste this link to share this article on your social media post.
2024-05-1601:30 PM
The ION8650 can support up to 10 Modbus Master TCP connections (which are completely separate from the 8 incoming connection restriction).
So if you have 8 separate IP addresses, this is supported presently. If you need more, I'd recommend daisy chaining some of the devices via RS-485 and gateway a few together.
But if you are implying that there are *eight* Modbus Master which want to access the ION8650, then the only recourse would be to likely use some type of Modbus gateway (like ComX or Link150 or HEP ION meter) and connect the ION8650 serially. The Modbus gateway will allow multiple masters to connect and alternate the requests sent to the ION8650.
Link copied. Please paste this link to share this article on your social media post.
2024-05-1601:30 PM
The ION8650 can support up to 10 Modbus Master TCP connections (which are completely separate from the 8 incoming connection restriction).
So if you have 8 separate IP addresses, this is supported presently. If you need more, I'd recommend daisy chaining some of the devices via RS-485 and gateway a few together.
But if you are implying that there are *eight* Modbus Master which want to access the ION8650, then the only recourse would be to likely use some type of Modbus gateway (like ComX or Link150 or HEP ION meter) and connect the ION8650 serially. The Modbus gateway will allow multiple masters to connect and alternate the requests sent to the ION8650.