Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Protecting our Community from Spam Events

Dear Members, we apologize for any disruption or inconvenience caused by the recent spam incidents, and we want to assure you that our dedicated team is actively investigating each reported instance of spam and implementing robust measures to mitigate the impact. Learn more on Spams Mitigation Guidelines

Thank you,

Schneider Electric Community Team

PM8000 Firmware Issue

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Firmware Issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
292
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
71
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-05-03 07:56 AM

0 Likes
27
6357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-03 07:56 AM

PM8000 Firmware Issue

I have a hands-on customer who has tried to upgrade the firmware in a PM82401 to v2.1 to enable waveforms to be viewed in the device web pages. Unfortunately, it has not worked and whatever has been done has affected the framework in the meter so it no longer displays all data in the web pages and 47 modules are off-line when the upgrade has been completed.

 

Fortunately this meter is not fully commissioned yet so is there a way to reset the meter to factory default so that he can can start over?

 

I have attached the screen captures taken from the upgrade.

 

Thanks

 

Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cliff_Schubert
Lieutenant JG Cliff_Schubert Lieutenant JG
Lieutenant JG

Posted: ‎2019-05-30 09:49 AM . Last Modified: ‎2019-05-31 10:26 AM

2 Likes
14
6301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-30 09:49 AM

The latest 2.1.0 firmware for the PM8000 MID meter is here:

https://www.schneider-electric.com/en/download/document/PM8000_MID_meter_FW_v2.1.0/

 

With ION Setup v3.1 you can choose the zip file for the upgrade which will allow you to program the meter firmware, web pages, and default template all from the one file.

 

You can upgrade directly from 1.1.0 to 2.1.0 using the zip file referenced above and ION Setup will perform any intermediate upgrades for you.

See Answer In Context

Reply
Robert_Lee
Captain Robert_Lee Captain
Captain

Posted: ‎2019-06-05 09:19 AM . Last Modified: ‎2019-06-05 09:24 AM

1 Like
8
6266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-05 09:19 AM

That's the wrong file.  It should be called TEMPLATE.LOG and should be located in the following folder:

C:\ProgramData\Schneider Electric\ION Setup

You might also want to also send us your SYSTEM.LOG file as well.

 

You might try to unzip the Web page zip file to a temporary file location and try to upload those files/folders using a FTP client (like WinSCP/FileZilla or even Windows Explorer).  If you are unable to connect to the FTP port, then its likely blocked by some type of networking equipment which you could try to bypass with a direct cross-over cable directly to the device (you would likely have to reprogram your laptop's IP address to one on the same subnet as the PM8000 at that point).

See Answer In Context

Reply
Cliff_Schubert
Lieutenant JG Cliff_Schubert Lieutenant JG
Lieutenant JG

Posted: ‎2019-07-08 09:21 AM . Last Modified: ‎2019-07-08 09:22 AM

2 Likes
1
6226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-08 09:21 AM

That message indicates the meter does not have any web pages loaded. The web page files are provided along with every firmware release. You can upload the meter web pages via FTP or using ION Setup.

 

There are instructions in this thread and also on page 188 in the PM8000 user guide: https://www.schneider-electric.ca/en/download/document/7EN02-0336/

See Answer In Context

Reply
Replies 27
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-05-03 09:26 AM

2 Likes
4
6353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-03 09:26 AM

Recommend going from V1.1 to V1.3 first before going to V1.4.3. There were some changes between V1.1 and V1.4.3 that could possibly make the upgrade have challenges. 

 

https://www.schneider-electric.ca/en/download/document/PM8000_V001.003.001.upg/

L4 Prime for Advanced metering and Utilities
Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-05-08 03:10 AM

0 Likes
3
6342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-08 03:10 AM

Hi

 

I tried the v1.3 upgrade but am still having problems with the RMP framework. What else can I try?

 

Thanks

 

 

Attachments
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-05-08 01:43 PM

0 Likes
0
6339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-08 01:43 PM

Recommend making sure you have the latest version of ION Setup, if you do have that, then will need to log a case with technical support. Be sure to include the log files from "C:\ProgramData\Schneider Electric\ION Setup"
Screen shot of the device settings, ION Setup -> select device -> Diagnostics -> General tab would also be a good idea.

L4 Prime for Advanced metering and Utilities
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2019-05-09 10:22 AM

0 Likes
1
6336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-09 10:22 AM

What framework version are you trying to RMP to your 1.3.1 firmware device?  (as per your ION Setup screen shot) - wondering if you not trying to get to 2.1.0, then do the RMP piece?

Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2019-05-15 08:30 AM

0 Likes
21
6329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-15 08:30 AM

@solutions_iems- Just want to confirm you have this resolved - thanks !

 

Tom

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-05-16 02:00 AM

0 Likes
0
6324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-16 02:00 AM

No not yet. Not had the opportunity to try as I'm bogged down with PME software issues at the moment. Thanks

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-05-16 02:15 AM

0 Likes
0
6320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-16 02:15 AM

What is the recommended firmware upgrade path from v1.1 to v2.1 and which RMP should be used?

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-05-29 06:46 AM

0 Likes
19
6312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-29 06:46 AM

Hi Tom

 

One PME issue resolved and one pending, so back to the PM8000 FW.

 

The meter is FW v001.001.000 as per attached but is not displaying all live data. What do I need to get this back to a functional device before I even consider upgrading the firmware to display waveforms in the web pages?

 

Thanks

Attachments
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2019-05-29 10:53 AM

0 Likes
18
6310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-29 10:53 AM

David Anderson on the firmware team here believes it sounds like an interrupted upgrade - the recommendation is to go to firmware version 1.4.3 first, then proceed with the upgrade to 2.1.0 again.

 

Tom 

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-05-30 01:15 AM

0 Likes
17
6307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-30 01:15 AM

I have upgraded the meter to v1.4.3 firmware and it has partially restored the meter functionality (see attached process and errors) but the meter still states that it is v1.1.0 in ION Setup and the Diagnostic web page.

 

I'm guessing that the missing functionality is down to the compatibility of the installed template (v1.4.0) with V1.1.0 firmware?

 

Should I now try upgrading to v2.1?

Attachments
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2019-05-30 08:37 AM

0 Likes
16
6305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-30 08:37 AM

Hmmm - it looks like you have a PM8000 MID meter, not a standard PM8000 - can you confirm?  The PM8000 and ION7400 have a different firmware file for MID.  The "NAK Target Not Supported" message is indicating this (wrong firmware file for this device type).  Looking at the messages, the 1.4.3 operation did not work for the same reason - you need the MID firmware.

 

@Cliff_Schubert 

 

 

 

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-05-30 08:40 AM

0 Likes
15
6303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-30 08:40 AM

It is the MID version (METSEPM82401).

 

Do you have a link to the MID F/W upgrade?

 

Thanks

Reply
Cliff_Schubert
Lieutenant JG Cliff_Schubert Lieutenant JG
Lieutenant JG

Posted: ‎2019-05-30 09:49 AM . Last Modified: ‎2019-05-31 10:26 AM

2 Likes
14
6302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-30 09:49 AM

The latest 2.1.0 firmware for the PM8000 MID meter is here:

https://www.schneider-electric.com/en/download/document/PM8000_MID_meter_FW_v2.1.0/

 

With ION Setup v3.1 you can choose the zip file for the upgrade which will allow you to program the meter firmware, web pages, and default template all from the one file.

 

You can upgrade directly from 1.1.0 to 2.1.0 using the zip file referenced above and ION Setup will perform any intermediate upgrades for you.

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-05-31 01:01 AM

0 Likes
13
6293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-31 01:01 AM

Thank you for the link to the upgrade file.

 

I have applied the upgrade and can confirm that it was 100% successful, however...

 

The web pages no longer work! - please see attached for details

Attachments
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2019-05-31 08:21 AM

1 Like
12
6289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-31 08:21 AM

That is good news !  For the web pages - just confirming you have the latest ION Setup.  If so, have you tried just re-uploading only the web pages?  In ION Setup, it's under "Template" in the wizard, "Web" tab, and then click the "Upload" button.  Tech support will be able to assist if needed - sounds like you are really close !  

 

If you have the latest ION Setup, can you post the log file here, so we can take a look - thanks !  @Robert_Lee 

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-06-03 09:31 AM

0 Likes
11
6278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-03 09:31 AM

Hi Tom

 

Yes I am using the latest version of ION Setup (v3.1.19095.01) and I have just tried uploading the web pages from the Template "Upgrade" and "Web" tabs but neither has made any difference.

 

Where will I find the ION Setup log file?

 

Thanks

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-06-03 09:40 AM

1 Like
10
6275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-03 09:40 AM

C:\ProgramData\Schneider Electric\ION Setup

 

May also be good to ftp to the meter and get a copy of the web files currently on the device.

L4 Prime for Advanced metering and Utilities
Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-06-05 07:30 AM

0 Likes
9
6270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-05 07:30 AM

There are no web files on the meter. All folders are empty.

 

Copy of ION Setup log attached.

Attachments
Reply
Robert_Lee
Captain Robert_Lee Captain
Captain

Posted: ‎2019-06-05 09:19 AM . Last Modified: ‎2019-06-05 09:24 AM

1 Like
8
6267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-05 09:19 AM

That's the wrong file.  It should be called TEMPLATE.LOG and should be located in the following folder:

C:\ProgramData\Schneider Electric\ION Setup

You might also want to also send us your SYSTEM.LOG file as well.

 

You might try to unzip the Web page zip file to a temporary file location and try to upload those files/folders using a FTP client (like WinSCP/FileZilla or even Windows Explorer).  If you are unable to connect to the FTP port, then its likely blocked by some type of networking equipment which you could try to bypass with a direct cross-over cable directly to the device (you would likely have to reprogram your laptop's IP address to one on the same subnet as the PM8000 at that point).

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-06-06 01:08 AM

0 Likes
7
6261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-06 01:08 AM

Template.log and System.log files attached for reference.

 

The great news is that by unzipping and copying the web page files direct to the meter using Windows Explorer and FTP has worked!!!!!!

 

Thank you all for your assistance with this matter 🙂

Attachments
SYSTEM.LOG
TEMPLATE.LOG
Reply
Robert_Lee
Captain Robert_Lee Captain
Captain

Posted: ‎2019-06-06 08:44 AM

0 Likes
6
6257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-06 08:44 AM

What OS version is running on the PC.  ION Setup is attempting to use PowerShell V3 (which should be available in most newer WIndows OSes), in order to automatically unzip the web zip file but I don't see an entry in the SYSTEM.LOG indicating that the unzip was successful.

 

Thursday, June 6, 2019 8:41:33 AM: UNZIP, Process, powershell.exe "& { Add-Type -A 'System.IO.Compression.FileSystem'; [IO.Compression.ZipFile]::ExtractToDirectory('C:\ProgramData\Schneider Electric\ION Setup\www\ION9000_webpages_000.001.925.zip', 'C:\Users\SESA70~1\AppData\Local\Temp\IONSET~2\web\'); }", Target, C:\Users\SESA70~1\AppData\Local\Temp\IONSET~2\web\

 

Something like the above entry should appear in the SYSTEM.LOG when you attempt to upload web pages clicking on the Upload button from the Web tab and you've selected the zip file (you would also see a dialog appear as it is uploading the individual files *IF* it is successful in unzipping.

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-06-06 09:04 AM

0 Likes
5
6254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-06 09:04 AM

Windows Server 2016 Data Center Edition

Reply
jan_opsteyn
Lieutenant | EcoXpert Master jan_opsteyn Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-07-08 05:33 AM

0 Likes
4
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-08 05:33 AM

After upgrading with latest ION software & PM8000 version V002.001.000

Login PM8000.png

Is there a solution to get the web server back?

Reply
Cliff_Schubert
Lieutenant JG Cliff_Schubert Lieutenant JG
Lieutenant JG

Posted: ‎2019-07-08 09:21 AM . Last Modified: ‎2019-07-08 09:22 AM

2 Likes
1
6227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-08 09:21 AM

That message indicates the meter does not have any web pages loaded. The web page files are provided along with every firmware release. You can upload the meter web pages via FTP or using ION Setup.

 

There are instructions in this thread and also on page 188 in the PM8000 user guide: https://www.schneider-electric.ca/en/download/document/7EN02-0336/

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2019-07-08 09:50 AM

0 Likes
0
6223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-08 09:50 AM

The issue is now resolved.

 

The PM8000 meter was the MID version but the firmware was for the non-MID version.

 

Once upgraded with the correct version (MID), the firmware upgrade to v2.1 was successful and the web pages and waveforms now all work correctly.

 

Thank you.

Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2019-07-22 02:54 PM

0 Likes
1
6197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-22 02:54 PM

You can try to upload just the web pages again using ION Setup or an FTP client - have your tried this?

 

Thanks


Tom

Reply
jan_opsteyn
Lieutenant | EcoXpert Master jan_opsteyn Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-07-22 11:00 PM

0 Likes
0
6190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-22 11:00 PM

Webpages are solved. 

uploaded by FTP the files.

 

Thanks

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc