PM8000 COMTRADE File Timestamp

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 COMTRADE File Timestamp
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
497
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
96
Robert_Lee
Admiral Robert_Lee Admiral
92
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2025-06-30 08:34 PM

0 Likes
3
105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-30 08:34 PM

PM8000 COMTRADE File Timestamp

Hi All,

 

I'm based in Taiwan (UTC+8) and recently encountered a timestamp issue while reviewing waveform data from a PM8000 meter.

 

When I view the COMTRADE file through the Webpage interface (and also the COMTRADE .dat file), the timestamp shows as:

 

2024/10/31 13:23:27

Stuart_Cheng_0-1751340599666.png

Stuart_Cheng_5-1751340677180.png

 

 

However, when I check the same event using CBEMA data, PME, or ION Setup, the timestamp is:

 

2024/10/31 21:23:27

Stuart_Cheng_1-1751340624218.png

 

Stuart_Cheng_2-1751340624224.png

 

Stuart_Cheng_3-1751340624234.png

 

Stuart_Cheng_4-1751340624245.png

 

 

This 8-hour difference makes me wonder:
Is the timestamp in the COMTRADE file recorded in UTC (UTC+0)?

If so, is there a way to configure the Webpage interface to display the COMTRADE timestamp in local time (UTC+8) instead?

 

Any insights or suggestions would be greatly appreciated. Thank you.

 

 

 

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-07-01 09:18 PM . Last Modified: ‎2025-07-01 11:08 PM

0 Likes
0
99
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-01 09:18 PM

Hi @Stuart_Cheng 

 

That is correct. The COMTRADE file is generated using UTC time, NOT local time, and this cannot be changed through the webpage because the COMTRADE format is based on UTC.

The webpage simply reads the time data directly from the COMTRADE file. However, the time can be manually modified within the file itself.

 

For more information, please check the following knowledge base article:
What is the PM8000's COMTRADE File Format and can it be changed?

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-07-02 07:36 AM

0 Likes
0
84
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-02 07:36 AM

Hello @Stuart_Cheng ,

 

Correct that the .cfg file for COMTREADE files use timestamps in UTC. When PME collects the data, the timestamp is also in UTC, however when PME displays the data, the UTC time is converted to local time during viewing the data.

 

The meter's webpage uses JavaScript to collect the data from the meter's internal file system to display the time. It could be possible to create a customized JavaScript file that takes the time and convert the time by X hours. Note that I do not have explicit instructions on how to do this nor do I have example files to share. The changes would be customizations that would not be officially supported.

 

Another option would be to submit a request to your local sales channel to submit a feature request to the global offer team to have a feature in future firmware release. Global offer team gets requests from around the world, not all requests will be included in future firmware. The request needs to come from sales who provide some business context to the request.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 3
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-07-01 09:18 PM . Last Modified: ‎2025-07-01 11:08 PM

0 Likes
0
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-01 09:18 PM

Hi @Stuart_Cheng 

 

That is correct. The COMTRADE file is generated using UTC time, NOT local time, and this cannot be changed through the webpage because the COMTRADE format is based on UTC.

The webpage simply reads the time data directly from the COMTRADE file. However, the time can be manually modified within the file itself.

 

For more information, please check the following knowledge base article:
What is the PM8000's COMTRADE File Format and can it be changed?

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-07-02 07:36 AM

0 Likes
0
85
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-02 07:36 AM

Hello @Stuart_Cheng ,

 

Correct that the .cfg file for COMTREADE files use timestamps in UTC. When PME collects the data, the timestamp is also in UTC, however when PME displays the data, the UTC time is converted to local time during viewing the data.

 

The meter's webpage uses JavaScript to collect the data from the meter's internal file system to display the time. It could be possible to create a customized JavaScript file that takes the time and convert the time by X hours. Note that I do not have explicit instructions on how to do this nor do I have example files to share. The changes would be customizations that would not be officially supported.

 

Another option would be to submit a request to your local sales channel to submit a feature request to the global offer team to have a feature in future firmware release. Global offer team gets requests from around the world, not all requests will be included in future firmware. The request needs to come from sales who provide some business context to the request.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2025-07-02 08:19 AM

0 Likes
0
82
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-02 08:19 AM

@Mehran_Mehrnia @Charles_Murison 

Clear, many thanks for your explanation!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of