Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Cannot connect to HDPM6000 after erroneously setting subnet mask 255.255.255.255

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Cannot connect to HDPM6000 after erroneously setting subnet mask 255.255.255.255
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
rcamacker
Crewman rcamacker Crewman
Crewman

Posted: ‎2025-02-26 10:46 AM

0 Likes
3
342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-26 10:46 AM

Cannot connect to HDPM6000 after erroneously setting subnet mask 255.255.255.255

Commissioning new HDPM6000. Updated firmware. Set client's requested IP but typo'ed 255.255.255.255 as the subnet mask. Cannot ping, open webpage, Modbus will not connect, no HDPM6000 Manager access. NetCfg can read the address but cannot change it as the firmware of the meter is too new.

Is there any way to change the submask remotely or otherwise connect to the meter?

Labels
  • Labels:
  • HDPM6000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
rcamacker
Crewman rcamacker Crewman
Crewman

Posted: ‎2025-02-26 07:43 PM

0 Likes
1
321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-26 07:43 PM

Thanks for the reply Mehran. Once I had erroneously changed the subnet mask to 255.255.255.255 there was no way to locally connect to the meter. Nothing worked, except NetCfg. However NetCfg could not change the IP address as this firmware was up-graded on the HDPM6000 (After a certain framework NetCfg cannot change the IP address). Had to join the site network to open the webpage.

See Answer In Context

Reply
Replies 3
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-02-26 12:43 PM

2 Likes
0
331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-26 12:43 PM

Hi @rcamacker 

 

The subnet mask of 255.255.255.255 likely has isolated the device from all other devices on the network.

Here are some steps that could help to resolve it:

1- If possible, connect your laptop directly to the meter using an Ethernet cable and assign a static IP address to your computer that is in the same subnet as the meter’s original configuration.

For example, if the meter was previously set to 192.168.1.x, set your computer to 192.168.1.10 and try to connect.

 

2- You mentioned 'Modbus will not connect' and I assume via Modbus TCP, but have you tried connecting serially to the device via a gateway or USB/Serial converter to read the Modbus registers from 4481 using any Modbus application to read the configured/saved IP address and subnet mask of this meter and try to edit them accordingly? 

In this example, I connected through Modbus(in my case via TCP) and wrote the values 255,255,0,0 to the registers 4489-4491:

Mehran_Mehrnia_0-1740602119596.png 

Mehran_Mehrnia_1-1740602255793.png

By default serial Modbus settings of HDPM6000 is as below:
Modbus Slave Address: 1
Baud rate: 115200
Parity: None

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
rcamacker
Crewman rcamacker Crewman
Crewman

Posted: ‎2025-02-26 07:43 PM

0 Likes
1
322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-26 07:43 PM

Thanks for the reply Mehran. Once I had erroneously changed the subnet mask to 255.255.255.255 there was no way to locally connect to the meter. Nothing worked, except NetCfg. However NetCfg could not change the IP address as this firmware was up-graded on the HDPM6000 (After a certain framework NetCfg cannot change the IP address). Had to join the site network to open the webpage.

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-02-27 11:05 AM

0 Likes
0
291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-27 11:05 AM

Hello @rcamacker ,

Likely when you connected the meter to the network, the meter was able to route traffic through the gateway address.

 

regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now