Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM800 vs PM8000 (register to register comparison)

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM800 vs PM8000 (register to register comparison)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2016-06-24 10:04 AM

1 Like
9
4673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-24 10:04 AM

PM800 vs PM8000 (register to register comparison)

I've been asked to match a clients PM800 register map to equivalent PM8000 registers.

I need help finding the equivalent PM8000 register for these PM800 items because I just can find tjem.

PM800 register:

1211     THD/thd Voltage, Phase A-B

1212     THD/thd Voltage, Phase B-C

1213     THD/thd Voltage, Phase C-A

1231     Current Fundamental Coincident Angle, Phase A

1233     Current Fundamental Coincident Angle, Phase B

1235     Current Fundamental Coincident Angle, Phase C

1245     Voltage Fundamental Coincident Angle, A-N/A-B

1247     Voltage Fundamental Coincident Angle, B-N/B-C

1249     Voltage Fundamental Coincident Angle, C-N/C-A

1961     Present Demand Current, Phase A

1971     Present Demand Current, Phase B

1981     Present Demand Current, Phase C

2151     Present Demand Real Power, 3-Phase Total

2166     Present Demand Reactive Power, 3-Phase Total

2181     Present Demand Apparent Power, 3-Phase Total


3214     Scale F – Power

8000     Requested Command

8001     Command Parameters

Thank you !

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa56307_bridg
sesa56307_bridg Troubleshooter
Troubleshooter

Posted: ‎2016-07-04 02:54 PM

4 Likes
1
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-04 02:54 PM

Hal is correct to point out that access to complex data (or advanced configuration) typically requires use of the ION protocol.  However, compared to previous ION meters, the PM8000 provides a much more comprehensive set of real-time values in its default Modbus map.  Most/all of the real-time values should now be present in the default Modbus map.  As a result, some of the registers that you are asking about do exist in the default Modbus map for the PM8000, although perhaps under a slightly different name.  But some of them do not exist on the meter at all, due to some small differences in implementation compared to the PM800.

I have provided my comments here on the specific registers from your original post, to the best of my knowledge.

1211     THD/thd Voltage, Phase A-B

1212     THD/thd Voltage, Phase B-C

1213     THD/thd Voltage, Phase C-A

[On the PM8000, the present implementation provides voltage harmonics for either line-to-neutral voltages or line-to-line voltages based on the wiring mode, but not both at the same time.  When the PM8000 is configured in 4W-WYE, 3W-WYE or SINGLE mode, it will provide voltage harmonics as line-to-neutral values.  When the PM8000 is configured in DELTA mode, it will provide voltage harmonics as line-to-line values.  The equivalent THD values in the PM8000 register list can be found at registers 21330, 21332 and 21334.  The published register list does look misleading to me, so I can understand the confusion.]

1231     Current Fundamental Coincident Angle, Phase A

1233     Current Fundamental Coincident Angle, Phase B

1235     Current Fundamental Coincident Angle, Phase C

1245     Voltage Fundamental Coincident Angle, A-N/A-B

1247     Voltage Fundamental Coincident Angle, B-N/B-C

1249     Voltage Fundamental Coincident Angle, C-N/C-A

[On the PM8000, all individual harmonics (up to the 63rd) are published in the register list, with values provided for both magnitude and angle.  The term "coincident angle" is not used in the PM8000 register list, so that might have made it harder to find.  You can find the H1 Angle registers for three-phase voltage and current at registers 22880, 23268, 23656, 24432, 24820, and 25208.]

1961     Present Demand Current, Phase A

1971     Present Demand Current, Phase B

1981     Present Demand Current, Phase C

2151     Present Demand Real Power, 3-Phase Total

2166     Present Demand Reactive Power, 3-Phase Total

2181     Present Demand Apparent Power, 3-Phase Total

[On the PM8000, there is no value provided for "present demand" (which on the PM800 was a type of accumulated integration over each demand interval).  Instead, the PM8000 provides registers for "Last Demand" (the value from the last completed demand interval), "Predicted Demand" (the value predicted for the end of the present demand interval based on the accumulation so far), and "Peak Demand" (the maximum of all the completed demand intervals since the last reset).  You can find these values in the Modbus map in the section starting around register 29884, which includes per-phase current demand, real/reactive/apparent power demand, and a number of other derivative cases.]


3214     Scale F – Power

8000     Requested Command

8001     Command Parameters

[On the PM8000, there is no direct equivalent for these ones.  As I understand, the "Scale F - Power" register is a scaling factor used for determining the proper scaling of an alarm setpoint related to power measurements.  Alarming is done differently on the PM8000 than the PM800, and while the equivalent function is still absolutely available the configuration of alarming is not done through Modbus.  Similarly, the other two registers here are related to the Modbus command interface, which is not present on the PM8000 (its functionality is replaced by the ION protocol, which is largely abstracted through the ION Setup configuration tool).]


As Hal explained, it may still be worth considering creating a custom Modbus map using the Modbus Slave modules, to remap the measurements of interest to match the PM800 map as closely as possible.  And any custom measurements added on top of the default ION framework will require this to expose them via Modbus.  But if you're looking to use the default Modbus map for the meter's default real-time measurements, most/all of the real-time values should be available.


Best regards,


David Tuckey

Firmware Architect


See Answer In Context

Reply
Replies 9
sesa213753
sesa213753 Leader
Leader

Posted: ‎2016-06-24 10:26 AM . Last Modified: ‎2022-10-18 10:36 PM

0 Likes
1
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-24 10:26 AM

Hi Gregory please check this -> https://community.se.com/message/74233#74233

Reply
Anonymous user
Not applicable

Posted: ‎2016-06-24 10:46 AM

0 Likes
0
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-24 10:46 AM

Thank you Jorge.   Actually that's the first post I read when I was looking for the PM8000 register list.

The problem I'm having is the points I'm looking for don't seem to be in that list.

Reply
Yut
Yut
Leader

Posted: ‎2016-06-28 12:40 AM

0 Likes
5
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-28 12:40 AM

I had a replacement job replaced the ION7300. I just simply rewrote the Modbus map of the PM8000  using ION7300 map then replaced the unit.

Reply
Anonymous user
Not applicable

Posted: ‎2016-06-28 06:58 AM

0 Likes
4
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-28 06:58 AM

Thanks Yut !   

I will suggest that to our client.

That will make his SCADA work more simple for sure.

The issue still is finding all the PM800 points in the PM8000.

For example the PM8000 register list doesn't show THD volts L-L, but I'm sure it's capable of this measurement.

Greg.

Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2016-06-28 11:54 AM

0 Likes
1
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-28 11:54 AM

Most ION devices calculate THD Volt L-L parameter but it probably is not be mapped to a Modbus register by default.  In that case you will need to link the register you wish to expose to a Modbus slave module (create a new or link to an existing one).  The Modbus slave module setup registers will define the Modbus register address the input register will be mapped to, the format of the register, etc.

For more information check out the ION Reference document as it will fully explain how the Modbus slave module works and they can be configured.

It is recommended to use the ION protocol in most cases with an ION device.  Modbus does not allow the download of any complex data measured by the device.  Exclusively exposing an ION device via Modbus is the equivalent of taking a high end sports car and replacing its engine with one from a golf cart.  The Modbus slave modules are meant for the application where only a few registers need to be exchanged with other software packages.

Reply
Matt_Curry
Matt_Curry Champion
Champion

Posted: ‎2016-06-28 12:23 PM

0 Likes
0
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-28 12:23 PM

ARNAUD DENIS, Cliff Schubert

Reply
michael_franz
michael_franz
Mentor

Posted: ‎2016-06-28 12:52 PM

0 Likes
0
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-28 12:52 PM

Have list but this page will not allow me to attach a file.............

Reply
sesa56307_bridg
sesa56307_bridg Troubleshooter
Troubleshooter

Posted: ‎2016-07-04 02:54 PM

4 Likes
1
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-04 02:54 PM

Hal is correct to point out that access to complex data (or advanced configuration) typically requires use of the ION protocol.  However, compared to previous ION meters, the PM8000 provides a much more comprehensive set of real-time values in its default Modbus map.  Most/all of the real-time values should now be present in the default Modbus map.  As a result, some of the registers that you are asking about do exist in the default Modbus map for the PM8000, although perhaps under a slightly different name.  But some of them do not exist on the meter at all, due to some small differences in implementation compared to the PM800.

I have provided my comments here on the specific registers from your original post, to the best of my knowledge.

1211     THD/thd Voltage, Phase A-B

1212     THD/thd Voltage, Phase B-C

1213     THD/thd Voltage, Phase C-A

[On the PM8000, the present implementation provides voltage harmonics for either line-to-neutral voltages or line-to-line voltages based on the wiring mode, but not both at the same time.  When the PM8000 is configured in 4W-WYE, 3W-WYE or SINGLE mode, it will provide voltage harmonics as line-to-neutral values.  When the PM8000 is configured in DELTA mode, it will provide voltage harmonics as line-to-line values.  The equivalent THD values in the PM8000 register list can be found at registers 21330, 21332 and 21334.  The published register list does look misleading to me, so I can understand the confusion.]

1231     Current Fundamental Coincident Angle, Phase A

1233     Current Fundamental Coincident Angle, Phase B

1235     Current Fundamental Coincident Angle, Phase C

1245     Voltage Fundamental Coincident Angle, A-N/A-B

1247     Voltage Fundamental Coincident Angle, B-N/B-C

1249     Voltage Fundamental Coincident Angle, C-N/C-A

[On the PM8000, all individual harmonics (up to the 63rd) are published in the register list, with values provided for both magnitude and angle.  The term "coincident angle" is not used in the PM8000 register list, so that might have made it harder to find.  You can find the H1 Angle registers for three-phase voltage and current at registers 22880, 23268, 23656, 24432, 24820, and 25208.]

1961     Present Demand Current, Phase A

1971     Present Demand Current, Phase B

1981     Present Demand Current, Phase C

2151     Present Demand Real Power, 3-Phase Total

2166     Present Demand Reactive Power, 3-Phase Total

2181     Present Demand Apparent Power, 3-Phase Total

[On the PM8000, there is no value provided for "present demand" (which on the PM800 was a type of accumulated integration over each demand interval).  Instead, the PM8000 provides registers for "Last Demand" (the value from the last completed demand interval), "Predicted Demand" (the value predicted for the end of the present demand interval based on the accumulation so far), and "Peak Demand" (the maximum of all the completed demand intervals since the last reset).  You can find these values in the Modbus map in the section starting around register 29884, which includes per-phase current demand, real/reactive/apparent power demand, and a number of other derivative cases.]


3214     Scale F – Power

8000     Requested Command

8001     Command Parameters

[On the PM8000, there is no direct equivalent for these ones.  As I understand, the "Scale F - Power" register is a scaling factor used for determining the proper scaling of an alarm setpoint related to power measurements.  Alarming is done differently on the PM8000 than the PM800, and while the equivalent function is still absolutely available the configuration of alarming is not done through Modbus.  Similarly, the other two registers here are related to the Modbus command interface, which is not present on the PM8000 (its functionality is replaced by the ION protocol, which is largely abstracted through the ION Setup configuration tool).]


As Hal explained, it may still be worth considering creating a custom Modbus map using the Modbus Slave modules, to remap the measurements of interest to match the PM800 map as closely as possible.  And any custom measurements added on top of the default ION framework will require this to expose them via Modbus.  But if you're looking to use the default Modbus map for the meter's default real-time measurements, most/all of the real-time values should be available.


Best regards,


David Tuckey

Firmware Architect


Reply
Anonymous user
Not applicable

Posted: ‎2016-07-22 11:28 AM

1 Like
0
4519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-22 11:28 AM

David,


THANK YOU for taking the time to research the answer to my question.

I really appreciate the thoroughness and commitment.

Cheers,


Greg.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore