Hi
Let me know PM5560 meter will support ring Topology.
If support then, which type of protocol will support MRP or RSTP
All the meters we are done in Daisy chain looping, Which type of communication is working background from the meter to meter communication .
By
Velu
Link copied. Please paste this link to share this article on your social media post.
Hello @Velu_Fajr
PM5500 series meters support only the straight line topology, does not support the ring topology.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @Velu_Fajr
PM5500 series meters support only the straight line topology, does not support the ring topology.
Regards,
Ramasamy N