Please could you elaborate on how the PM5110 calculates neutral current when there is no direct connection ?
I recall from another post that it uses a vector sum formula.
Are you able to add any more detail ? thanks
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes, The neutral current is calculated value using vector sum formula in PM5110.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @Ramasamy_N ,
Do you know the answer to this question? I would think either sample by sample calculation or vector sum calculation.
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes, The neutral current is calculated value using vector sum formula in PM5110.
Regards,
Ramasamy N