PM5560 Firmware and Webpages

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5560 Firmware and Webpages
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Anonymous user
Not applicable

Posted: ‎2020-09-17 12:47 AM

0 Likes
12
5392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-17 12:47 AM

PM5560 Firmware and Webpages

I don't often configure meters but had to setup an PM5560 on the network for some BACnet testing and when i went to the web pages i was met with the below, when did this change, is there no way of changing these settings in the web pages ?

 

Also ION Setup does not give access to the comms setup, the only thing available is Modbus RTU settings, this means to change a config on a meter in the field you have to be at the meter, this isn't ideal

 

Or am i missing something ?

 

2020-09-17_08-41-12.jpg

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2020-09-18 03:41 AM

3 Likes
8
5370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-18 03:41 AM

You can refer the KBA article that attached in my previous comment for more details on Compliance to Senate Bill 327 or SB-327 which may not applicable for EMEA region. But the Schneider Electric’s Cyber security policies (https://www.se.com/ww/en/work/solutions/cybersecurity/) which applicable for all region. 

 

The ION setup version v3.2.20127.03 and above added the "IP com support" option for PM5560 firmware version v2.7.8.

 

 
 

IP com setup.JPG

 

You can edit the BACnet setting from "IP Comm setup" menu as below, 

Bacnet settings.JPG

 

Let me know if you have any other issue for changing the BACnet settings.

 

Regards, 

Ramasamy N

 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2022-03-01 03:53 AM

2 Likes
6
4570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-01 03:53 AM

Hello @Thumudi_TD 

 

The BACnet settings must filled with some values for Device ID and BBMD IP (same IP address of meter) when we try to change some parameter in BACnet settings. 

 

 
 
 

 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 12
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-09-17 02:17 PM

0 Likes
11
5382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-17 02:17 PM

@Ramasamy_N  do you know the answer?

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2020-09-18 01:12 AM

1 Like
10
5378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-18 01:12 AM

Hi @Anonymous user 

 

Yes, the PM5500 series does not support the configuration settings from meter web page from the firmware version v2.7.8 to comply with the California 2020 law and SE cyber security guidelines. The alternate way to configure this settings is use ION setup latest version. Please refer the attached KB article for more details. 

 

Regards, 

Ramasamy N 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2020-09-18 01:31 AM . Last Modified: ‎2020-09-18 01:32 AM

0 Likes
9
5374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-18 01:31 AM

Thanks, I'm not sure which California 2020 Law you are referring to or how that is applicable to the EMEA region but will read your attachment

 

Correct me if I'm wrong but ION Setup on the PM5560 does not give you access to BACnet, Ethernet and other comms settings etc. all that seems to be available is RS485 settings ?

 

Thanks

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2020-09-18 03:41 AM

3 Likes
8
5371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-18 03:41 AM

You can refer the KBA article that attached in my previous comment for more details on Compliance to Senate Bill 327 or SB-327 which may not applicable for EMEA region. But the Schneider Electric’s Cyber security policies (https://www.se.com/ww/en/work/solutions/cybersecurity/) which applicable for all region. 

 

The ION setup version v3.2.20127.03 and above added the "IP com support" option for PM5560 firmware version v2.7.8.

 

 
 

IP com setup.JPG

 

You can edit the BACnet setting from "IP Comm setup" menu as below, 

Bacnet settings.JPG

 

Let me know if you have any other issue for changing the BACnet settings.

 

Regards, 

Ramasamy N

 

 

Tags (1)
  • Tags:
  • english
Reply
Thumudi_TD
Lieutenant | EcoXpert Master Thumudi_TD Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-03-01 02:26 AM

0 Likes
7
4576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-01 02:26 AM

@Ramasamy_N I have ION IONSetup v3.2.22033.01 working on PM5560 OS 2.7.8 i tried on 2 meters with the same software version and i get invalid parameter when i try to send config over ION Setup.meter Firmwaremeter Firmwareerror when sending configs to metererror when sending configs to meterdisabling via ION Setupdisabling via ION Setup

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2022-03-01 03:53 AM

2 Likes
6
4571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-01 03:53 AM

Hello @Thumudi_TD 

 

The BACnet settings must filled with some values for Device ID and BBMD IP (same IP address of meter) when we try to change some parameter in BACnet settings. 

 

 
 
 

 

 

Tags (1)
  • Tags:
  • english
Reply
Thumudi_TD
Lieutenant | EcoXpert Master Thumudi_TD Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-03-01 05:30 AM

0 Likes
5
4565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-01 05:30 AM

thanks i can now Enable and Disable.

Tags (1)
  • Tags:
  • english
Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2022-03-01 02:29 PM

0 Likes
4
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-01 02:29 PM

I'm curious to how/why these settings got set to "invalid" setting.  Was this meter field upgraded or was received from the factory in that manner?  There have been instances where firmware has previously allowed invalid settings to be initialized (typically on firmware upgrade), at which point ION Setup will not automatically fix that issue until the user tries to edit those fields.

Tags (1)
  • Tags:
  • english
Reply
Thumudi_TD
Lieutenant | EcoXpert Master Thumudi_TD Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-03-01 10:22 PM

0 Likes
3
4553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-01 10:22 PM

Factory Firmware, And when BACnet is disabled on the HMI some meters on the webpage still shows BACnet Enabled while HMI is showing Disabled. And ION showing Disabled however on EBO the ES or AS-P can still See meters with Duplicate ID's and kicked out as non-conferment Devices. Disabling 300 meters onsite is tedious. 

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2022-03-02 08:05 AM

0 Likes
0
4545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-02 08:05 AM

Hello @Thumudi_TD 

 

This seems to be an issue in the firmware version v2.7.8 with ION setup. 

 

However, the latest firmware v4.1.3 allows user to control the protocol option in the meter webpage itself. 

You can download firmware file from below path, 

https://www.se.com/in/en/download/document/PM5560_PM5563_PM5580_V4.1.3/ 

 

Hello @Robert_Lee 

 

The default device ID was 0 in v2.7.8 and it was corrected as last 5 digit of meter serial number in the firmware v4.1.3

 

Regards, 

Ramasamy N

 

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2022-03-04 01:46 AM

0 Likes
1
4537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-04 01:46 AM

Hello @Thumudi_TD 

 

I just simulated this condition with ION setup and the PM5560 v2.7.8 in our lab meters, 

The BACnet protocol status is updating properly in the meter HMI and the Webpage. There is no mismatch between the HMI and webpage in the protocol status. 

 

Is the meter sending the pockets to EBO even when the BACnet status is displaying as "Disabled" in the HMI? 

Can you check after configuring the unique BACnet device ID all the meters? 

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
Thumudi_TD
Lieutenant | EcoXpert Master Thumudi_TD Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-03-04 04:30 AM

0 Likes
0
4533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-04 04:30 AM

once you add an ID number and disable the BACnet on HMI it stops sending pockets to EBO. with default ID 0 and BACnet Disabled it send Pockets. 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now