Continue
  • My Subscriptions
  • Events
ION8650 9/29/36S in a 36S Base
Metering & Power Quality
  • EcoStruxure Power & Grid
  • ION8650 9/29/36S in a 36S Base
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
PowerLogic
PowerLogic ION8650 series
Nicholas_Brown
Nicholas_Brown Explorer
Explorer
Posted: ‎2022-03-02 07:20 AM
3
2492
Hi, My customer is questioning if the ION8650 in a 36S base will show all phase related reading similar to a 9S base.  I know for a 36S base, the B phase voltage is not wired, but my assumption is the Vbn and kWb will be calculated.  Is this correct or are there limitations when placed in a 36S base.  Thanks.
  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
View products (1)
Charles_Murison
Champion
Posted: ‎2022-03-03 08:24 AM
1
2467
Hello @Nicholas_Brown ,
As long at the meter's Volts mode 36S - 4 Wire Wye is selected, yes the B phase voltage and power will be calculated. Vb = -(Va+Vc).
Charles
Charles_Murison
Champion
1
2467
Charles
DanL
DanL Champion
Champion
Posted: ‎2022-03-03 10:25 AM
Yes.
The ION8650 in volts mode "36S - 4 Wire Wye" (with 2 PTs) presumes the Zero sequence symmetrical component magnitude = 0.
The meter computes the "B phase" instantaneous voltage (ie. waveform) as Vbn = -(Van + Vcn)
The meter computes the "B phase" instantaneous power as Pb = -(Van x Ib + Vcn x Ib) = Vbn x Ib
Nicholas_Brown
Explorer
Posted: ‎2022-03-03 05:22 PM
Thank you for your reply, I appreciate the help.