Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5560 Connection Issue with ION Setup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5560 Connection Issue with ION Setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
ABDUL8
ABDUL8
Explorer

Posted: ‎2025-08-03 09:51 PM

0 Likes
6
3044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-03 09:51 PM

PM5560 Connection Issue with ION Setup

I'm having trouble connecting the PM5560 meter (latest firmware v4.4.8) with ION Setup (v3.2.25185.01) using the Single ION Device Configuration Mode. However, it works fine when I connect to the PM8000 or ION9000. Is this mode only meant for ION devices?  I can still access the meter via the webpage. Any thoughts or advice to get PM5560 working with IONSetup would be much appreciated.

Attachments
Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Sidharthan
Sidharthan Contributor
Contributor

Posted: ‎2025-08-04 03:51 AM

1 Like
0
3034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 03:51 AM

Single ION Device Configuration Mode is for ION devices only,

Please follow this FAQ000259425 How to add a device into ION Setup | Schneider Electric India
To add PM5560 device in ION Setup.

See Answer In Context

  • Thumbnail of PowerLogic PM5000 series
    Schneider Electric
    PowerLogic PM5000 series
View products (1)
Tags (1)
  • Tags:
  • Add Ethernet based devices to ION Setup
Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2025-08-07 01:50 PM

0 Likes
1
2983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-07 01:50 PM

The PM5560 is not an ION Device (so there is no Setup Assistant).  Almost all Basic Metering offers are Modbus based and do not communicate using ION protocol (which is why Single ION Device mode doesn't work and why there are no Setup Assistant).

See Answer In Context

Reply
Replies 6
Sidharthan
Sidharthan Contributor
Contributor

Posted: ‎2025-08-04 03:51 AM

1 Like
0
3034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 03:51 AM

Single ION Device Configuration Mode is for ION devices only,

Please follow this FAQ000259425 How to add a device into ION Setup | Schneider Electric India
To add PM5560 device in ION Setup.

  • Thumbnail of PowerLogic PM5000 series
    Schneider Electric
    PowerLogic PM5000 series
View products (1)
Tags (1)
  • Tags:
  • Add Ethernet based devices to ION Setup
Reply
ABDUL8
ABDUL8
Explorer

Posted: ‎2025-08-04 04:23 PM

1 Like
0
3023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 04:23 PM

Thanks, Sidharthan it works.

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2025-08-05 04:19 PM

1 Like
0
3008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-05 04:19 PM

The "Single ION Device Configuration mode" as stated in the name is for ION Device only (otherwise I would of called it just "Single Device Configuration mode").

Most Basic Meter products (like the PM5000 series) are Modbus based and would also require either a port selection option to be available (since most use port 502 instead of port 7700/7443) or slow down scanning as it would have to alternate between ION and Modbus protocols when done serially (modems are not even viable using Modbus connections).

Reply
ABDUL8
ABDUL8
Explorer

Posted: ‎2025-08-06 10:32 PM . Last Modified: ‎2025-08-06 10:35 PM

0 Likes
0
2994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-06 10:32 PM

Thanks, Robert and Sidhartan.
Another issue I’ve encountered is when I add the PM5560 in ION Setup—it only shows the advanced settings, and the setup assistant icon disappears.

 Screenshot 2025-08-07 125418.pngIs there any way to get the setup assistant to appear?

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2025-08-07 01:50 PM

0 Likes
1
2983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-07 01:50 PM

The PM5560 is not an ION Device (so there is no Setup Assistant).  Almost all Basic Metering offers are Modbus based and do not communicate using ION protocol (which is why Single ION Device mode doesn't work and why there are no Setup Assistant).

Reply
ABDUL8
ABDUL8
Explorer

Posted: ‎2025-08-07 04:22 PM

0 Likes
0
2978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-07 04:22 PM

Thanks Robert, that explains!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore