Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5350 Sliding Window Demand - half hour logging

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5350 Sliding Window Demand - half hour logging
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
swil
swil
Mentor

Posted: ‎2020-11-03 08:17 PM

0 Likes
5
3251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-03 08:17 PM

PM5350 Sliding Window Demand - half hour logging

Hi,

 

A PM5350 is being as a main meter with the Billing Module. It needs to be configured to do have sliding window demand (kVA) over 30 minute intervals instead of (default) 15 minute intervals.

 

If PME software logging is set to 30 minutes for the Block Demand kVA parameter (quantity id 37 in PME), will the parameter logged be 30 minute SWD kVA, or will it be 15 minute SWD kVA every 30 minutes?

 

 

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2020-11-05 12:57 PM

2 Likes
1
3235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-05 12:57 PM

In ION Setup, device setup select Demand Setup -> Power Demand -> Periods/Sub-Interval can change it from 15 minutes to 30 minutes.

I believe you can also do it via the front panel display as well.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2020-11-04 12:05 PM

1 Like
0
3245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-04 12:05 PM

Using SW logging for billing purposes is probably not a good idea.  If logged data is required for billing purposes then use on-board logging so the data will be accurately logged right on the interval boundary.

 

SW logging does *not* log on the interval boundary.  It periodically polls the list of realtime registers and the last value read before the interval boundary is what is logged.  Depending how the device driver is configured this could be a realtime value from several minutes before the interval boundary.

 

The SWD intervals are independent.  Thus if you need 30 min intervals then change the meter configuration to be 30 minutes.  Logging the 15 minute interval every 30 minutes will only give a picture of what happened in the previous 15 minutes (ie 15 minutes will be missing).

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-11-04 04:51 PM

0 Likes
3
3241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-04 04:51 PM

@Ramasamy_N , do you know of a way to change the demand windows from 15 to 30 minutes?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2020-11-05 12:57 PM

2 Likes
1
3235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-05 12:57 PM

In ION Setup, device setup select Demand Setup -> Power Demand -> Periods/Sub-Interval can change it from 15 minutes to 30 minutes.

I believe you can also do it via the front panel display as well.

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2020-11-05 05:59 PM

0 Likes
0
3229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-05 05:59 PM

Yes, Charles, 

 

We can change the demand interval from 1 to 60 minutes using ION setup or meter HMI. The demand value will be calculated and updated every 15 seconds (if the demand interval is less than 15 minutes) or updated every 60 seconds (if the demand interval is more than 15 minutes)

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
swil
swil
Mentor

Posted: ‎2020-11-09 12:58 AM

0 Likes
0
3223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-09 12:58 AM

Thank you.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore