ION9000 Power Factor difference

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
mauricio_rojas_
Crewman
Crewman
0 Likes
2
604

ION9000 Power Factor difference

Hello everybody

 

Im looking for some guidance about an ION9000. The client has installed the meter in a LV system (3-Wire Grounded Wye) with a common current transformer with a sentronpac 3200. 

 

 
 

capture layout ion9k.PNG

 1. For power Factor, there are a big difference about the total factor (0.96 for ION9000 and 0.75 for sentronpac). We put a portatil meter (Fluke 435) and the Fluke reads also 0.75.  Is there any problem for the Total Power Factor in ION9000?  About the Current readings, the two meters have the same values.

 

2. About the ION9000 installation manual, we see that for 3-Wire Grounded Wye, there is only a MV graphic like below:

l.PNG

In order to correct the problem. How do we have to wire the meter  and its possible to fix the error in the total power factor reading?

 

 

Thanks in advance

 

Tags (1)

Accepted Solutions
DanL
Commander Commander
Commander

Re: ION9000 Power Factor difference

Issue 1: The LV system is described as a 3-wire grounded WYE. Let's assume that PTs are not used and the voltage wired to the meter is <690VLL. The best correct wiring and VOLTS mode to use would be the direct connect 4W-WYE where the meter's VN measuring terminal is connected to the common ground point of the power system.

Issue 2: The "Total Power Factor" on all ION meters is the ratio of the "Total kW" and the "Total kVA". Most likely they have the default configured "kVA Tot Method" = "Vector sum". The other device is likely implementing the equivalent of "Scalar Sum".

A large discrepancy is typical with non-linear loads or distorted signals.
IONReference\PowerMeterModule 

 

See Answer In Context

Tags (1)
2 Replies 2
Charles_Murison
Picard Picard
Picard
0 Likes
1
599

Re: ION9000 Power Factor difference

Hello @mauricio_rojas_ ,

 

Looking at the data provided I am surprised to see the total PF so different from the individual phases. Where are you reading these numbers, software, web pages front panel? What are the readings for kw and kVA per phase and total? What is the kVA calculation method?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
DanL
Commander Commander
Commander

Re: ION9000 Power Factor difference

Issue 1: The LV system is described as a 3-wire grounded WYE. Let's assume that PTs are not used and the voltage wired to the meter is <690VLL. The best correct wiring and VOLTS mode to use would be the direct connect 4W-WYE where the meter's VN measuring terminal is connected to the common ground point of the power system.

Issue 2: The "Total Power Factor" on all ION meters is the ratio of the "Total kW" and the "Total kVA". Most likely they have the default configured "kVA Tot Method" = "Vector sum". The other device is likely implementing the equivalent of "Scalar Sum".

A large discrepancy is typical with non-linear loads or distorted signals.
IONReference\PowerMeterModule 

 